[RE-wrenches] Midnite solar Charge controllers
boB at midnitesolar.com
boB at midnitesolar.com
Mon Feb 17 23:30:38 EST 2014
All CC's have their problems and MidNite has had their share, but losing
or forgetting their programming has not
been one of them that I'm aware of.
If it is a standard Classic with MNGP display, don't forget to press
ENTER after setting parameters so that
the Classic remembers those settings if the DC goes off and back on again.
I would give Ryan call in tech support. extension 151.
boB
On 2/17/2014 8:06 PM, Jerry Shafer wrote:
> Has anyone had an issue with Midnite solar Charge controllers loosing
> programming. I have had Out back FM 80 do this and it was an software
> issue they fixed it. Now I have the same thing with midnite either
> that or the customer is messing with it and this is also a good
> possibility but before I go there I want to confirm with you all out
> there. The issue from Outback is if the CC is powered down on both
> sides it will loose memory, I cant confirm this as the customer is
> away and I cant get on site but we have Nickle Iron batteries that
> require high charge voltage to charge at all and it seams to not
> maintain the charge voltage setting.
>
> Thanks
> Jerry
>