[RE-wrenches] AC Back feed from Radian.
Ray Walters
ray at solarray.com
Mon Feb 17 17:30:59 EST 2014
Alot of these generator setups need 2 regulators, so usually the regular
one stays at the tank, size the pipe for the flow rate ( just like wire
and amps....;-) .) and put the 2nd regulator right at the generator.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 2/17/2014 3:17 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
> Ditto Tom, seen this too often in Mexico. I carry a manometer to make
> check the pressure at the _LP input to the generator with the engine
> running_. Make sure it is at/above 11" WC when it starts to act up. If
> the regulator is at the tank, long vapor runs can cause too much
> pressure loss.
>
> Larry
>
>
>
> On Feb 17, 2014, at 1:36 PM, Tom Duffy <Tom at thesolar.biz
> <mailto:Tom at thesolar.biz>> wrote:
>
> Hi Guys
> We have had "icing" problems here in Central America as well where the
> gas company put in ½' pipe to a 12K Gillette Generator, same
> description the gen would initially start and run fine but then it
> went erratic the Radian didn't like it, the customer wanted to blame
> the Radian (I was sure it wasn't)
> The installer/dealer couldn't figure it out. I went out and
> immediately saw the small pipe, plus they had bent a crimp into the
> incoming fuel line as well. ¾" line fixed the whole thing. LP has a
> lot of moisture and will always have delivery problems with funky
> installation of pipe. Seems that a lot of gas guys just hook up
> kitchen ranges (Here)
> Kind regards
> *Tom Duffy*
> *Senior Solar Design Engineer*
> <image002.png>
> *E-Mail:**tom at thesolar.biz <mailto:tom at thesolar.biz>*
> *Panama Office:**507-6126-1253*
> *Direct Toll Free:**888-503-6772*
> *International:**575-539-2111*
> *SKYPE Address:**thesolarbiz*
> /Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced./
> *Confidentiality Notice*:This message including any attachments is for
> the sole use of the intended recipient and may contain confidential
> and privileged information. Any unauthorized review, use, disclosure
> or distribution is prohibited. If you are not the intended recipient,
> please contact the sender and delete any copies of this message.
> **
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140217/b11139f1/attachment.htm>
More information about the RE-Wrenches
mailing list