[RE-wrenches] DC Fusing/Breakers for Battery Circuits

frenergy frenergy at psln.com
Sat Feb 8 16:52:31 EST 2014


So help me out with a little more detail please.  Example (Dan's configuration and my current in-progress install):  2 Strings of 8, L-16s for 48V. nom.  Destination: the common pos bus at the bottom of a pair of 125 amp CBs as OCP for 2, VFX3648s.  

        Positive battery current path: from each end of both battery string pos terminals, the next stop would be a (110 amp?) Class T fuse, one for each cable/string.  Then cables from each of these fuses would land on one Bus (hefty chunk of copper bar stock) mounted on inside of battery box (backed up with Dan's cement board), combining the outputs of both batt strings.  From this one bus, run 2 cables to the pos bus at the bottom of the 2, 125 Amp CB's (in this case provided in the OB-DC Flex enclosure, protecting the 3648s.

        A little simpler (better?) would be to just bolt the Class T fuses right to the bus in the battery box, eliminating some cable.  Feedback?...and thanks,

Bill
Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax

  ----- Original Message ----- 
  From: Dan Fink 
  To: Allan Sindelar ; RE-wrenches 
  Sent: Saturday, February 08, 2014 12:05 PM
  Subject: Re: [RE-wrenches] DC Fusing/Breakers for Battery Circuits


  Allan;
  It's a topic much on my mind recently and i will provide a writeup soon. It's all very well documented. I do have photos, but they don't show the fire damage to the wooden battery box unfortunately, the client was a bit flustered getting all the batteries out of there after the incident and when I showed up he had already demo-ed the box. But the photos of the batteries themselves do tell the story rather well. 
  There was another issue also.....his Xantrex power panel was wired with a 'self destruct switch' main battery cutoff. I did not design or install the panel. But his logical reaction in seeing smoke coming out of his battery box was to open the main battery disconnect breaker on the panel, which then put solar 140vdc onto the inverters  inputs. Both were zorched by high voltage. He should have opened the solar breaker first, then the main DC. His homeowner's unsurance did cover most of it all.
  The batteries were 8 years old....end of lifespan situation.
  Lessons learned......OCP on parallel battery strings, and cement board liner in all battery boxes, if they are field built wooden.


  Dan Fink,
  Executive Director;
  Otherpower
  Buckville Energy Consulting
  Buckville Publications LLC
  NABCEP / IREC accredited Continuing Education Providers
  970.672.4342

   



  On Fri, Feb 7, 2014 at 10:36 AM, Allan Sindelar <allan at positiveenergysolar.com> wrote:

    Dan,
    Do you have a writeup on that event? Any photos? I have many plywood battery enclosures in the field.
    Thanks,

    Allan


    Allan Sindelar
    Allan at positiveenergysolar.com
    NABCEP Certified PV Installation Professional
    NABCEP Certified Technical Sales Professional
    New Mexico EE98J Journeyman Electrician
    Founder, Positive Energy, Inc.

    A Certified B CorporationTM
    3209 Richards Lane
    Santa Fe, New Mexico 87507
    505 424-1112 office 780-2738 cell
    www.positiveenergysolar.com



    On 2/7/2014 10:26 AM, Dan Fink wrote:

      Does anyone have any elegant solutions to this? It's really time consuming and ugly to run big parallel battery string wires *out* of the battery enclosure to class T fuses, then back into the battery box. It looks very ugly and DIY, and in conduit adds a few hundred to the install cost just for labor. The Class T fuses and blocks themselves are not particularly expensive. 
      I have been recommending parallel fusing on battery banks of 2x8 L16s and over now, after a nearly tragic incident with a bad cell that shorted. The (perfectly legal) wooden battery box made the fire much worse. A pet peeve of mine. 




      Dan Fink,
      Executive Director;
      Otherpower
      Buckville Energy Consulting
      Buckville Publications LLC
      NABCEP / IREC accredited Continuing Education Providers
      970.672.4342



       

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org







------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches at lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140208/dcfdd810/attachment.htm>


More information about the RE-Wrenches mailing list