[RE-wrenches] DC Fusing/Breakers for Battery Circuits
Dave Click
daveclick at fsec.ucf.edu
Thu Feb 6 17:23:08 EST 2014
All,
I think that in the past, list discussions have talked about fusing of
parallel battery circuits as a best practice, but it's required per
690.9 right? (text below from 2008 NEC)
Also, if someone (don't look at me) really wants to use 2 parallel
circuits of 12V batteries, what equipment is recommended to provide
overcurrent protection? The installer is using Outback hardware (FW500?)
and has two battery circuits combined in the battery enclosure and run
to a Big Bus feeding the two 125A dc disconnects for two GVFX3648s. If
you've read this far, this area is more your wheelhouse than mine.
Thanks in advance!
690.9 Overcurrent Protection
(A) Circuits and Equipment. Photovoltaic source circuit, photovoltaic
output circuit, inverter output circuit, and storage battery circuit
conductors and equipment shall be protected in accordance with the
requirements of Article 240. Circuits connected to more than one
electrical source shall have overcurrent devices located so as to
provide overcurrent protection from all sources.
Exception: An overcurrent device shall not be required for circuit
conductors sized in accordance with 690.8(B) and located where one of
the following apply:
(a) There are no external sources such as parallel-connected source
circuits, batteries, or backfeed from inverters.
(b) The short-circuit currents from all sources do not exceed the
ampacity of the conductors.