[RE-wrenches] Satcon Inverter in need of help!

Allen Frishman amfrish at aeonsolar.com
Thu Jan 30 14:24:45 EST 2014


Wrenchers,
Looking for some support on a 75KW Satcon inverter that is 3 years old.   System went down with Fault Code "66" gate fdbk B - The action is "Contact Satcon Services"


Spoke with a guy at PV Inverter Services that was helpful and he diagnosed the issue as the IGBT that needs to be replaced.    Looking for additional contacts to check with on availability and price for this part.    Also will appreciate any feedback from others that have dealt with this Fault.   Hoping someone has dealt with this issue and found a simple fix but I realize that is not likely.

All info is appreciated.

Thanks!
Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com