[RE-wrenches] NEC 2014 690.12 Rapid Shutdown
Drake
drake.chamberlin at redwoodalliance.org
Tue Jan 21 12:36:15 EST 2014
Bill,
It is good to see that energized conductors are
going to be disconnected near the arrays. I've
been an advocate of disconnecting these
conductors by ground fault sensing equipment
since ground fault detection was first
implemented in the code. If contactors are to be
installed on roofs, it likely won't be long
before both ground faults and arc faults are automatically cleared.
When the requirement for AC arc fault branch
circuit protection was first put in the NEC, it
was postdated to allow time for the electrical
industry to adapt. This new remote disconnecting
requirement does not provide any lead time.
As the 2014 NEC is adopted in various
jurisdictions, inspectors may feel that it is
necessary to disallow systems without the newly
required disconnect feature. This may result in
serious problems for solar companies and customers, as well as manufacturers.
The protection of firefighters is essential. The
implementation of renewables is essential also.
Insurance claims for weather related, global
warming-triggered climatic disasters are rising
exponentially. Extreme weather related events
result in major loss of life and billions of
dollars in property damage. Atmospheric CO2
levels continue to climb from the burning of
fossil fuels. This is a crisis of global proportions.
My request for code writers is to please take
into account the effect that inserting new rules
into the NEC may have on the stability of
renewable energy, and implement new requirements
in a way that will allow for a smooth interface.
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
At 12:45 PM 1/16/2014, you wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_0F94_01CF129F.BCC65BD0"
>Content-Language: en-us
>
>Jeffrey,
>
>Sounds like you need to get involved in the code
>making process since you have so many good ideas
>on how to improve the language. I like
>confrontational discussions as long as they lead
>to a better understanding and constructive outcomes.
>
>About 30 people worked on this language, so it
>is definitely not perfect. However, I dont
>think it is quite as bad as you make it out to
>be. I wanted to jump in since some of your conclusions were not correct.
>
>This is a circuit requirement, not a
>disconnecting means requirement, since it has to
>do with shock hazard of PV circuits in and
>around a building. This is for firefighter
>safety. 30V is the international standard for
>touch safe in a wet location. 240VA is to set a
>limit on the available power on a circuit.
>Contactor combiners, which would be part of a
>compliant solution, have 24V control circuits.
>The other reasoning for 240VA is that
>internally, 72-Cell PV modules can be divided
>into segments of this power level for the
>foreseeable future (more on that another day).
>
>If the conductors stay outside, you have 10
>from the array to place your shutdown device. On
>large central systems, this would likely be a
>contactor combinermost manufacturers sell
>these. If the conductors are going immediately
>into the building, as with residential and
>integrated systems, a shutdown device would have
>to be within 5 of entering the building. If
>goes outside for a while, then inside the
>building, the total length could be no more than
>10 and no more than 5 inside the buildingthis
>is not additive. Remember, all this is for firefighter safety.
>
>As Brian Mehalic and others have pointed out,
>the language does not specify where the shutdown
>initiating device is to be located. The lack of
>detail is more for flexibility than it is to
>give an AHJ license to make an installer do anything they want.
>
>With grid-tie only systems (no battery backup),
>it would be most convenient and cost effective
>to have a system that initiates the shutdown on
>loss of utility. In this way, a firefighter can
>do what they normally do, shut down utility
>power to the building, and the rapid shutdown
>would automatically initiate. This does not
>necessitate an additional disconnecting means
>for a load-side PV connection. The main breaker
>could be the initiating device. For a
>supply-side connection, the NEC already requires
>that the PV disconnect switch be located
>adjacent to the service disconnecting means (article 230).
>
>The biggest issue with string inverters (central
>inverters) is that there is a need to shutdown
>the capacitor input side of the inverter since
>that stays energized for 5 minutes or more. The
>10 seconds was to provide a means to rapidly
>discharge the capacitors rather than requiring a
>relay or tripping device. Doing something other
>than a relay will require a test laboratory to
>evaluate the functionguess what?we dont have
>a standard yet to evaluate those products.
>Sounds like you might want to work on that committee.
>
>It is more complicated for battery backup
>systems. Midnite Solars birdhouse products are
>the best I have seen so far to address this
>concern. Since dc and ac circuits are not
>differentiated, battery backup systems need to
>have a shutdown process that works independently
>of a utility outage for obvious reasons, and it
>must shutdown both the dc circuits and the
>backup ac circuits. A separate switch, like the
>birdhouse, would be necessary that only controls
>these functions in an emergency situation.
>
>Is the language not detailedpossibly. This was
>done to provide flexibility rather than create
>problems. Fire departments have been requiring
>rooftop disconnects for years in California.
>These disconnects are nearly worthless from a
>shock prevention point of view since capacitors
>in the inverter stay charged or there are
>multiple disconnecting means feeding each other.
>We have been trying to hold the fire community
>off of rooftop disconnect requirements so we
>could work on a solution that actually does what
>they want it to do. There is a long discussion
>on this in the appendix of my Understanding the
>CalFire Guidelines document on the SolarABCs website.
>
>The 2014 NEC language was a compromise worked
>out with the solar industry (yes string inverter
>companies as well) in response to the first
>version of the proposal which was to require
>module-level shutdown. This is not module-level
>shutdown, it is PV output circuit shutdown
>(combiner box shutdown is another way to look at
>it). However, the 2017 NEC cycle is this year
>and there was a lot of talk about requiring
>module-level shutdown this time around.
>
>I hope this helps. I will be writing articles
>for IAEI journal and other periodicals on this
>subject since it was a very far-reaching and
>potentially confusing new requirement in the
>NEC. Thanks for your interest and lets keep the
>constructive dialogue going on the subject. It
>is time to get involved in the NEC update process again.
>
>Bill Brooks.
>
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org]
>On Behalf Of Jeffrey Quackenbush
>Sent: Thursday, January 16, 2014 1:09 AM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
>
>Wrenches,
>
>There is no guidance in the Code text for where
>the shutdown should take place. (1) says:
>"Requirements for controlled conductors shall
>apply only to PV system conductors of more than
>1.5m (5') in length inside a building, or more than 3m (10') from a PV array."
>
>
>So, the provisions apply if the circuit 10' from
>the array and 5' inside a building, but no
>mention is made of where the shutdown actually
>needs take place in the circuit. In the video
>Bill Brooks suggests that the shutdown mechanism
>should also be placed within this 10'/5'
>boundary but that is just an inference --
>nowhere in the text is this actually specified.
>If that was the intent of the Code committee,
>then they've done a poor job actually expressing it in English.
>
>I'm concerned that some AHJs will interpret this
>to exclude all central inverter systems (without
>the addition of cost-inducing secondary DC-DC
>converters like Tigo) because the combiner or
>junction box can be many feet from the actual
>beginning of a home run under the array.
>Alternately, permissive AHJs could allow this
>function to be fulfilled anywhere, meaning that
>the implementation won't meet the intent of the writers.
>
>I'm also concerned, as Isaac mentioned, that
>there are no requirements for how the shutdown
>be initiated, or that it contains of the
>accessibility and grouping requirements that are
>always included for disconnects. I really think
>this should be treated and categorized as a
>disconnect requirement, not a circuit
>requirement, because that is the ultimate function that's intended.
>
>I'm surprised none of the inverter manufacturers
>have chosen to comment here, as this could
>dramatically impact the sales of central inverters.
>
>Jeffrey Quackenbush
>
>
>
>
>----------
><http://www.avast.com/>
>[]
><http://www.avast.com/>
>
>This email is free from viruses and malware
>because <http://www.avast.com/>avast! Antivirus protection is active.
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140121/83dd4b03/attachment.htm>
More information about the RE-Wrenches
mailing list