[RE-wrenches] Xantrex XW system stability
Eric.Bentsen at schneider-electric.com
Eric.Bentsen at schneider-electric.com
Mon Aug 26 10:27:50 EDT 2013
Hi Kevin,
We have found that network (Cat5) cables shorter than 2m (6.5 ft) causes
network reflections that contribute to network instability in multi-unit
XW systems. Do not rule out a bad or intermittent network cable either.
Also, confirm the inverters have the same firmware and the latest.
It is not necessary to have the controllers in-network, but it allows
Enhanced Grid operation, which does a better job of keeping batteries full
when
selling. For off grid, they can be in a separate network if you want to
monitor them with a dedicated SCP, but you will need to supply network
power
for Xanbus (AUX port can be used for this).
Rgds,
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
"Kevin Pegg" <kpegg at energyalternatives.ca>
To:
"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date:
08/22/2013 10:18 AM
Subject:
[RE-wrenches] Xantrex XW system stability
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Hello Wrenches,
Curious how others are finding the stability of larger Xantrex XW
deployments? We have an installation with 12 Xanbus devices (4 x XW6048, 6
x XW-MPPT60, 1 x AGS, 1 x SCP) and it keeps crashing. Power cycle the
whole system and it's fine for a few weeks and then it crashes again.
I find with smaller deployments under 5 Xanbus devices the stability is
much better, but still get the occasional customer call with a system gone
haywire and a power cycle fixes.
This particular installation is in the high arctic darn near the north
pole and sending a tech up there next week to resolve. Needless to say,
it's an expensive ordeal to get up there.
Kevin
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130826/c1029c4c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130826/c1029c4c/attachment-0001.jpe>
More information about the RE-Wrenches
mailing list