[RE-wrenches] double insulated wire
Bill Brooks
billbrooks7 at yahoo.com
Fri Jun 28 21:21:04 EDT 2013
Dave,
To add to your point, the typical way to wire an ungrounded PV system is to
use modules with PV Wire-connect them to homeruns of PV Wire-then transition
at some point to standard wire in raceways. This means that the only change
from a wiring method point of view is to use PV Wire wherever you used to
use USE-2 (like my multiple uses of USE in a sentence?-I think we have the
basis for a new Dr. Seuss book).
Now for my real bombshell-There are no ungrounded PV systems being installed
in the U.S. today that I am aware of. But what about all those non-isolated
"TL" inverter systems? The array cannot be grounded with a "TL" inverter
because the system becomes grounded the moment it connects to the grid. So
is it an ungrounded system or a grounded system. I could easily argue this
both ways and be wrong and right at the same time.
So what is an ungrounded PV system. A truly ungrounded PV system is one
where neither the positive, nor the negative are referenced directly to
earth. This is common in Europe for large inverters. The ground-fault
detection is done by putting an insulation monitor on the array that runs
24/7. You can't put an insulation monitor on a non-isolated inverter system
because it will trip the moment it connects to the grid.
Last bombshell-All grid-connected PV systems currently being installed in
the U.S. are not ungrounded and they are not solidly grounded. They are all
actually employing an alternative to both grounded and ungrounded from
690.41-"shall use other methods that accomplish equivalent system protection
in accordance with 250.4(A) and that utilize equipment listed and identified
for the use " I really love the irony that my friends like John Wiles and
others have been tooting the horn of grounded systems for so long, but our
systems are not solidly grounded (because of the ground-fault fuse). The
more-correct term for our systems is "functionally grounded", but even that
does not fully cover it. I'm writing a document on this presently-I've never
had so much fun with grounded in my life.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Friday, June 28, 2013 11:04 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] double insulated wire
690.35(D) does not require PV WIRE be used for the whole dc circuit. You can
use either: (quoting directly from 2008)
1) Nonmetallic jacketed multiconductor cables
2) Conductors installed in raceways, or
3) Conductors listed and identified as PV WIRE installed as exposed, single
conductors
Similarly, I don't believe that the NEC requires red and black color coding,
either, though it makes the most sense given convention.
Note Brian Teitelbaum's 6/3 email about PV WIRE noting that
"double-insulated" is a bit of a misnomer. Some PV WIRE is single-insulated.
DKC
On 2013/6/28 13:47, aram at aramsolar.com wrote:
In ungrounded systems the PV wire requirement is to be used the whole DC
circuit, so that is all the way to the inverter. 690.35 (D) is pretty clear
. Because it is ungrounded the protection is the PV wire's fire rating and
you don't get that with thhn/thwn.
And of course Red for positive and black for negative.
Most building departments have not pick up on this yet. But they will.
Aram
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130628/73719f82/attachment-0001.htm>
More information about the RE-Wrenches
mailing list