[RE-wrenches] pump questions

Louis Woofenden louis at woofenden.net
Fri May 31 13:40:02 EDT 2013


Hi Todd (and Allen & Bob-O),

You can also do the pump sizing online, using WebCAPS from Grundfos, if 
you don't have a PC handy: <http://net.grundfos.com/Appl/WebCAPS>, then 
click on "Sizing," and "Renewable Energy Systems". You'll still need to 
enter module data, since their database only includes their modules. You 
can also select locations, units, etc. like in the PC version.

Best,
Louis

On 5/31/13 10:30 AM, Allan Sindelar wrote:
> Bob-O and Todd,
> In theory you're right, Bob-O. I find the program awkward to use, 
> given that it thinks in some weird (Danish?) way, that I don't use 
> often enough to remember how to navigate. But in this case my bigger 
> concern would be how to input data for a bunch of old used Astropower 
> 75s. Astropower's been gone for over ten years, I think, and data 
> isn't likely to show up on the backsheets. WINCaps doesn't account for 
> module degradation, either.
>
> Todd, I might have a copy of a module spec sheet for the AP75 in our 
> files at the office. Not sure, as we never used any, but I collected a 
> lot of that old crap. Contact me off list on Monday if you need me to 
> look.
> Allan
>
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> *Positive Energy, Inc.*
> 3209 Richards Lane (note new address)
> Santa Fe, New Mexico 87507
> *505 424-1112*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
> *
> *
>
>
> On 5/31/2013 11:14 AM, Bob-O Schultze wrote:
>> Todd,
>> The easiest way to do this is to use the Grundfos pump sizing 
>> software. Regrettably, it only runs on a PC. You can input the specs 
>> of the module, the head and the GPD desired and it will size the 
>> array for you. Once you know the # of modules in series you can use 
>> the Imp and Vmp derated for temperature which will get you in the 
>> right ballpark for sizing the conductors. Won't be accurate, but 
>> close 'nuff.
>> Good Luck, bob-O
>>
>> On May 30, 2013, at 3:29 PM, Todd Cory wrote:
>>
>> this question is part 2 about the customer with the used astropower 
>> 75 watt modules -
>>
>> he has a grundfos 11sqf-2 already set by the well driller. the input 
>> specifications for the cu200 pump & controller are 30 to 300 vdc, 
>> 1400 watts, 8 amps.
>>
>> this will initially be running array direct and i am trying to figure 
>> out the wire loss from the modules to the cu200 controller. to do 
>> that i need voltage and current numbers. im assuming the higher the 
>> voltage the lower the running current?
>> from the specs above: 1400 watts divided by 8 amps = 175 volts... so 
>> if i feed this with closer to 300 volts would that mean the running 
>> current would drop to around 4.6 amps?
>>
>> thanks for the help,
>>
>> todd
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org 
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130531/58d7cfbd/attachment-0001.htm>


More information about the RE-Wrenches mailing list