Actually, one is the manufacturer closest to you, Paul- the Solectria 
SGI 225-500kW class does a 600VAC output.

On 2013/5/15 14:03, Paul Lyons wrote:
>
> Stump the RE-Wrenches:
>
> You know the NPR radio show, Car Talk, when they play "Stump the 
> Chumps"?  I visited a manufacturing plant last week that has a 13.8 kV 
> primary service that is stepped down to 600 VAC secondary by an indoor 
> 1500 A transformer and distributed around the plant to the large 
> pieces of equipment.  There is a small transformer for 240/120 
> single-phase devices in the relatively small office area.
>
> Do any of you know where I can find a UL-listed 3-phase inverter in 
> the 300 kW range that can be interconnected to the 600 VAC buss? 
>  There is a spare 600 A breaker. Feel free to contact me off the list. 
>  Thank you.
>
> Paul Lyons, P.E.
>
> Zapotec Energy Inc.
>
> 675 Massachusetts Ave
>
> Cambridge, MA 02139-3309
>
> Tel: 617-547-5900  ext.201
>
> Email: Lyons at ZapotecEnergy.com <mailto:Lyons at ZapotecEnergy.com>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130515/b4a1f0e0/attachment-0001.htm>


More information about the RE-Wrenches mailing list