[RE-wrenches] Question re fine stranded cable with Sunny Islandinverters

John Berdner John.Berdner at solaredge.com
Fri Mar 15 21:46:07 EDT 2013


Alan:

Use a ferrule on the inverter end of the wire.
Makes fine strand cable suitable for "normal lugs"

Burndy has some that they say are for fine strand (Class K) cable.
http://www.burndy.com/products/new-products/bare-ferrules.aspx

They look exactly the same as the cheaper un-insulated ferrules from ferrules direct.
http://www.ferrulesdirect.com/

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Friday, March 15, 2013 3:58 PM
To: RE-wrenches
Subject: [RE-wrenches] Question re fine stranded cable with Sunny Island inverters

Wrenches,
A small issue, drawing on the collective wisdom here:

For an upcoming quad-stack installation of Sunny Island inverters, I foolishly ordered some fine stranded copper 1/0 Cobra X-Flex Cable because of its flexibility. In this situation, because of NEC ampacity requirements on our total DC cabling (this system also has a single Radian for some dedicated loads) we are only running 125 amp DC breakers on each SI inverter.
Our issue is that the SI installation manual specifically notes not to use fine stranded cable into the terminal lugs. This was news to me. We can purchase 1/0 Ilsco or Panduit copper pigtail adapters to make the connection into the terminals of the inverters, but they are $10 to $14 each, and we need eight of them.
Is using doubled up #4 or #2 the only solution? Are there any other suggestions that will allow us to use the 1/0 X-Flex?
Thank you,
Allan
-
Allan Sindelar
Allan at positiveenergysolar.com<mailto:Allan at positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>






CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P  Please think of the environment before printing this email
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130316/fc18c9da/attachment-0001.htm>


More information about the RE-Wrenches mailing list