[RE-wrenches] Batteries and customer service
William Miller
william at millersolar.com
Fri Mar 15 18:55:16 EDT 2013
Lou:
Allan presents the better advice below. Ignore my previous post until you
are sure the battery is bad.
William Miller
At 02:57 PM 3/15/2013, you wrote:
>Lou,
>There is nothing in your message that definitively tells me that you have
>either a bad cell or a bad battery. "Minor corrosion on one terminal" is
>normal behavior, especially if the installer didn't coat the terminals at
>installation. "One cell was not using as much water as all the rest" is a
>matter of perception. You write yourself that "everything looked fine." It
>seems to me that you're jumping to conclusions based on the comment of
>another Wrench without doing sufficient testing first. Get the client to
>put a measured load on the system without charge. This isn't hard to do
>with an amp-hour meter in the system - you want a steady load of about 55
>A (a C/20 load). If you have a bad cell, it'll show up soon enough.
>
>For now, I'm on Interstate's side.
>
>Hope this helps,
>Allan
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130315/f309b7e4/attachment-0001.htm>