[RE-wrenches] finding array ground faults
Bill Brooks
billbrooks7 at yahoo.com
Wed Feb 6 09:52:06 EST 2013
Marco,
This should be fairly straightforward. If the whole roof is truly grounded,
you have nothing to worry about. If it is not well grounded, then you have
cause for pause.
I would recommend the new Megger MIT410 (or420 or 430) device. It has a 50V
setting which is hugely beneficial for testing surge arrestors as well as PV
arrays.
I assume this does not have an obvious fault, or you would not have asked.
If you can't find it with a dry megger, it is time to get out the garden
sprayer with a mild soap solution and start spraying down the array
methodically, one section at a time, while someone else operates the megger.
With all that grounded metal, it should be easy to find. Ground is your
friend when searching for ground faults.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Tuesday, February 05, 2013 9:57 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] finding array ground faults
Hoo boy....I've got a tough one here. Trying to troubleshoot an array
ground fault with a system that has 14 strings mounted on a metal roof with
the whole roof and metal framed building being common to ground.
Can anyone recommend any diagnostic tools out there to troubleshoot and
locate ground faults?
Thanks,
marco
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130206/d16dd60f/attachment-0001.htm>
More information about the RE-Wrenches
mailing list