[RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility question

Phil Undercuffler solarphil at gmail.com
Fri Feb 1 14:55:57 EST 2013


OutBack's Radian does AC input support, which can be applied to either a
generator or even to grid.

Phil


On Thu, Jan 31, 2013 at 5:19 PM, John Berdner <John.Berdner at solaredge.com>wrote:

>  SMA Sunny Island also does this but also discharges battery in parallel
> with the generator to create a “virtual generator” that is larger than the
> actual generator.****
>
> Just set the max generator current and it does the rest.****
>
> ** **
>
> Best Regards,****
>
> ** **
>
> John Berdner****
>
> General Manager, North America****
>
> ** **
>
> [image: SmallBannerPictEngnew]****
>
> ** **
>
> SolarEdge Technologies, Inc.****
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA  *(*Please note of our new
> address.)*
> T: 510.498.3200, X 747****
>
> M: 530.277.4894 ****
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Allan Sindelar
> *Sent:* Thursday, January 31, 2013 2:14 PM
> *To:* William Miller
> *Cc:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility
> question****
>
> ** **
>
> William,
> Yes, that's my understanding. Outback acknowledged this to me years ago.
> Allan****
>
> *Allan Sindelar*
> Allan at positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> *Positive Energy, Inc.*
> 3209 Richards Lane (note new address)
> Santa Fe, New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com ****
>
> ** **
>
> ** **
>
> On 1/29/2013 9:28 PM, William Miller wrote:****
>
> Allan:
>
> Could it be that the SW systems are protecting the generator with
> Generator Support, and the Outback inverters are not?
>
> William Miller
>
>
>
> At 07:18 PM 1/29/2013, you wrote:
>
> ****
>
> This is going back several years...
>
> The Outback VFX series lacks the tight input current regulation of the SW
> series, so the max AC amps in is really just a suggestion. In many cases
> (and especially with these small generators) we want to set the max amps in
> as high as possible to minimize charging time and maximize C/rate. Yet a
> surge load can momentarily exceed the max amps setting.
>
> I have observed that the Honda inverter/generators have a quite sensitive
> AC output breaker, that will sometimes trip if a surge load (such as a
> refrigerator) comes on during a charge cycle set close to the generator's
> capacity. This incident was specific to a Honda 3000i. In contrast,
> Yamaha's EF3000iSE will lug when overloaded - not good for the generator,
> but also not likely to trip the output breaker.
>
> This is a different issue than was being discussed, but fits your question.
> Allan****
>
> ** **
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
> for the use of the individual or entity who is the intended recipient and
> may contain information that is privileged, confidential and exempt from
> disclosure or any type of use under applicable law. If the reader of this
> e-mail is not the intended recipient, or the employee, agent, or
> representative responsible for delivering the e-mail to the intended
> recipient, you are hereby notified that any dissemination, distribution,
> copying, or other use of this e-mail is strictly prohibited. If you have
> received this e-mail in error, please reply immediately to the sender.
>
> *P*  Please think of the environment before printing this email
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130201/63a22314/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 13992 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130201/63a22314/attachment-0001.jpg>


More information about the RE-Wrenches mailing list