[RE-wrenches] Dc Power Supply on Microinverter input
John Berdner
John.Berdner at solaredge.com
Tue Jan 29 17:32:23 EST 2013
Mark:
Depends on the supply and the micro.
One or the other has to have isolation or bad things can happen.
Check with the manufacturers to see if the devices are isolated.
You could also use an isolation transformer ahead of the DC supply and be ok.
You might also need to float the ground on the supply (be careful).
Lastly the control loops in the mico and the supply probably won't play well together.
You can end up getting weird oscillations between the control loops in the MPPT and the CV/CI control of the supply.
You might need to add some resistance and typically some inductance between the supply and the inverter to get it to track right.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, January 29, 2013 11:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Dc Power Supply on Microinverter input
Folks,
Anyone have an idea of what would happen if I connected a bench top DC power supply with adjustable voltage and current to the pv inputs of a microinverter that is also connected on the Ac side? Would something bad happen as the inverter tries to run it's mppt on the ps?
Mark Frye
Berkeley Solar Electric Systems
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P Please think of the environment before printing this email
More information about the RE-Wrenches
mailing list