We have had no problems using WEEBs to bond inverters to rails and then
WEEB Lugs to run #6 bare as our GEC in area AHJs. One thing we are seeing
in systems installed by others is lack of proper bonding between rail
sections. We use WEEB Jumpers, which are great, if not a bit expensive. It
definitely makes longer rail sections more cost effective. The Unirac
splices are mechanical, not electrical bonding components. We've had no
problem with inspectors. In fact, we point out our WEEB Jumpers to gently
make the point that others are not doing it. Gotta level the playing field.
:)
I don't see any difference between a mechanically connected bonding wire in
a WEEB Lug and a mechanical lug on the inverter case. Either way, that
connection is reversible. The GEC itself must be continuous, such that
removing a device does not break the bond. We just hit each rail with a
single WEEB Lug. It makes for a much cleaner installation.
Regarding the rails as part of the GEC, Unirac rails are UL 2703 listed,
which I believe covers mounting systems as bonding devices. This is not my
area of expertise, so I'd like some confirmation on this.
*Jason Szumlanski** *
*Fafco Solar*
*
*
On Wed, Jan 16, 2013 at 1:17 PM, John Berdner <John.Berdner at solaredge.com>wrote:
> Mark:****
>
> ** **
>
> I agree that the Code requirement for GEC in grid tied PV makes no sense.*
> ***
>
> I have been trying to get it changed since the 2005 Code cycle.****
>
> Until it does change (not even likely in 2014) we are stuck with it …
> unless you float the array J****
>
> ** **
>
> Best Regards,****
>
> ** **
>
> John Berdner****
>
> General Manager, North America****
>
> ** **
>
> [image: SmallBannerPictEngnew]****
>
> ** **
>
> SolarEdge Technologies, Inc.****
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA *(*Please note of our new
> address.)*
> T: 510.498.3201 ext 747****
>
> M: 530.277.4894 ****
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Mark Frye
> *Sent:* Wednesday, January 16, 2013 10:08 AM
> *To:* re-wrenches at lists.re-wrenches.org
>
> *Subject:* Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ** **
>
> I believe the WEEB is a great product for producing equipment grounds. But
> for producing a GEC I don't see it. Even if I bond the inverter case to the
> rail with a WEEB what is the next step in the chain, a reversible WEEB lug
> to bond the rail to the wire. Still, I don't think the GEC for these
> microinverters is a rational requirement. It appears from the discussion
> that if I have a seperately installed microinverter that bonds it's DC side
> to ground, the Code requires a GEC but if I take that exact same inverter,
> assemble it to a module and test and list them as an AC module the
> requirement for GEC goes away. This is another indicator that the
> application of this requirement in the Code itself is specious.
>
> Mark Frye****
>
> On 1/16/2013 9:53 AM, John Berdner wrote:****
>
> Brain:****
>
> ****
>
> Not trying to be argumentative here…****
>
> ****
>
> I understand that you feel that a WEEB is equivalent to an irreversibly
> spliced connection but, as most commonly used in the field, I disagree.***
> *
>
> The Code does not recognize bolted connections of any kind as equivalent
> to irreversible spliced or contiguous.****
>
> It is an issue of the type of connection not the presence of the WEEB clip
> in that connection.****
>
> For Example: If the WEEB connection was riveted in place then I believe it
> would be considered irreversibly spliced but as part of a bolted
> connection, no.****
>
> ****
>
> With specific reference to GEC see 250.64C in the 2011 NEC or 2011 NEC
> Handbook. ****
>
> ****
>
> Lastly, the argument that it is a similar level of difficult to cutting
> the wire, while true, is not relevant to the Code requirement. Cutting a
> contiguous wire is also a similar level of difficulty to opening a bolted
> connection but obviously a bolted connection is not a contiguous wire.****
>
> ****
>
> Best Regards,****
>
> ****
>
> John Berdner****
>
> General Manager, North America****
>
> ****
>
> [image: SmallBannerPictEngnew]****
>
> ****
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA *(*Please note of our new
> address.)*
> T: 510.498.3201 ext 747****
>
> M: 530.277.4894 ****
>
> ****
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [
> mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
> *On Behalf Of *August Goers
> *Sent:* Wednesday, January 16, 2013 9:22 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ****
>
> Thanks Brian. This has been a helpful thread for me. Mark Frye, thanks for
> kicking it off.****
>
> ****
>
> Best, August****
>
> ****
>
> ****
>
> August Goers****
>
> ****
>
> Luminalt Energy Corporation****
>
> 1320 Potrero Avenue****
>
> San Francisco, CA 94110****
>
> m: 415.559.1525****
>
> o: 415.641.4000****
>
> august at luminalt.com****
>
> ****
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Brian Wiley
> *Sent:* Tuesday, January 15, 2013 1:02 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ****
>
> Hi August,
>
> I maintain that the WEEB is an irreversible splice.
> If you want to disconnect a WEEB from a structure, you must irreversibly
> damage the device. It cannot be reused.
>
> Admittedly the force required to remove a WEEB is less than that required
> for a thermal splice, but it doesn't take much force to just cut a wire
> either.
>
> I would argue that the intent of the code is to prevent inadvertent
> removal of the ground. You must knowingly remove a WEEB from the grounding
> path and if you do so in the maintenance of an array, good workmanship
> requires that you restore the connection. ****
>
> Best Regards,
> Brian Wiley****
>
> ****
>
> On 1/15/2013 2:11 PM, August Goers wrote:****
>
> Hi John,****
>
> ****
>
> I definitely see your point and that is why I was somewhat questioning the****
>
> use of WEEBs with Enphase below. Enphases's instructions (link posted in****
>
> thread below) seem to indicate a support of running the continuous GEC on****
>
> the rack and then bonding the microinverter to the rack with WEEBs. Maybe****
>
> I am misinterpreting the document or perhaps Enphase has another take.****
>
> There is no question that according to NEC 250.64(C) the GEC must be****
>
> continuous. In the 2008 NEC handbook section 690.42 Point of System****
>
> Grounding Connection has an application note "Connections are to be made****
>
> in accordance with markings on the equipment or in the installation****
>
> instructions."****
>
> ****
>
> All that said, it seems like technology is leaning towards listed AC****
>
> Modules or floating array inverters. It sounds like that removes the****
>
> requirement for a GEC which is great to help reduce installation costs.****
>
> The GEC has always been a pain in the neck.****
>
> ****
>
> Best,****
>
> ****
>
> August****
>
> ****
>
> ****
>
> -----Original Message-----****
>
> From: re-wrenches-bounces at lists.re-wrenches.org****
>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org <re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of John****
>
> Berdner****
>
> Sent: Monday, January 14, 2013 7:07 PM****
>
> To: RE-wrenches****
>
> Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ****
>
> August:****
>
> ****
>
> The WEEB or other Listed grounding means between the inverter case and the****
>
> structure are not "contiguous or irreversible spliced" and therefore do****
>
> not meet the requirements for a GEC.****
>
> If the structure is then grounded via a bolt on lug it also is not****
>
> irreversible or contiguous.****
>
> If you can unbolt something and disconnect the ground then it is not****
>
> contiguous or irreversibly spliced.****
>
> Both of the above are ok for EGC but not for GEC.****
>
> ****
>
> GEC is a pain in the neck but the Code requirements are clear.****
>
> If the PV array conductor (pos or neg) is bonded to ground by the inverter****
>
> then the inverter requires a GEC with all the related requirements - no if****
>
> and's or but's.****
>
> ****
>
> Best Regards,****
>
> ****
>
> John Berdner****
>
> General Manager, North America****
>
> ****
>
> SolarEdge Technologies, Inc.****
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new****
>
> address.)****
>
> T: 510.498.3201 ext 747****
>
> M: 530.277.4894****
>
> ****
>
> ****
>
> -----Original Message-----****
>
> From: re-wrenches-bounces at lists.re-wrenches.org****
>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org <re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of August****
>
> Goers****
>
> Sent: Monday, January 14, 2013 4:32 PM****
>
> To: RE-wrenches****
>
> Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ****
>
> Hi Mark,****
>
> ****
>
>
> There have been some recent threads on this list touching on this topic.****
>
> ****
>
> As far as I understand, Enphase microinvertes still require a GEC up to****
>
> and including the 2011 NEC. I don't know about the 2014 NEC. Enphase bonds****
>
> the positive DC module conductor to ground. Pages 16 and 17 of their M215****
>
> installation manual address grounding:****
>
> ****
>
> http://enphase.com/wp-uploads/enphase.com/2011/06/Enphase_M215_Installatio****
>
> nOperation_Manual.pdf****
>
> ****
>
> Products such as Solar Bridge that are listed as Alternating Current (AC)****
>
> Modules (per NEC 690.2) don't need a Grounding Electrode Conductor (GEC)****
>
> as long as there are no conductors connected to ground within the product.****
>
> Solar Bridge has a good article on this:****
>
> ****
>
> http://solarbridgetech.com/microinverters-and-ac-pv-modules-are-different/****
>
> ****
>
> This all takes us back to using Enphase with grounding washers like WEEBs****
>
> for the GEC. According to what I read in their instructions (and after****
>
>
> many phone calls), it sounds like they are okay with us running the GEC on****
>
> the racking in #6 and then bonding the microinverters to the rack with****
>
> WEEBs. Seems a little strange but it's been working for us.****
>
> ****
>
> Good topic!****
>
> ****
>
> Best,****
>
> ****
>
> ****
>
> August****
>
> 415.559.1525****
>
> ****
>
> ****
>
> -----Original Message-----****
>
> From: re-wrenches-bounces at lists.re-wrenches.org****
>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org <re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Mark Frye****
>
> Sent: Monday, January 14, 2013 3:31 PM****
>
> To: RE-wrenches****
>
> Subject: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules****
>
> ****
>
> Does anyone have the latest on the GEC for micro-inverters/ACPV issue?****
>
> ****
>
> I know it is still in NEC 2008 and I believe 2011 with plans to address it****
>
> in 2014.****
>
> ****
>
> I am specifically interested in the issue of GEC means continues****
>
> (irreversible splices) and the whole business of the DC side of these****
>
> devices constituting a separately derived system.****
>
> ****
>
> Enphase technical support is fine if the micro inverter chasis is bonded****
>
> to a EGC only, but they leave the lug on the chasis if you want/need to****
>
> build a GEC.****
>
> ****
>
> SolarBridge (pre-assembled micro-inverter) seems to be devoid of a chasis****
>
> lug and therefore by extension does not/can not had a GEC in the system.****
>
> ****
>
> Exeltech (integrated micro-inverter aka. ACPV) does not seem to have a lug****
>
> on its chasis.****
>
> ****
>
> ****
>
> Has the industry pretty much moved to not requiring a GEC for these****
>
> devices and if so, how are the AHJ taking it?****
>
> ****
>
> Thanks,****
>
> Mark Frye****
>
> Berkeley Solar Electric Systems****
>
> _______________________________________________****
>
>
> List sponsored by Home Power magazine****
>
> ****
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ****
>
> Options & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ****
>
> ****
>
> List-Archive:****
>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ****
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ****
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
> ****
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ****
>
> Options & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ****
>
> ****
>
> List-Archive:****
>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ****
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ****
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> ****
>
> ****
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only****
>
> for the use of the individual or entity who is the intended recipient and****
>
> may contain information that is privileged, confidential and exempt from****
>
> disclosure or any type of use under applicable law. If the reader of this****
>
> e-mail is not the intended recipient, or the employee, agent, or****
>
> representative responsible for delivering the e-mail to the intended****
>
> recipient, you are hereby notified that any dissemination, distribution,****
>
> copying, or other use of this e-mail is strictly prohibited. If you have****
>
> received this e-mail in error, please reply immediately to the sender.****
>
> P Please think of the environment before printing this email****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
>
> ****
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ****
>
> Options & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ****
>
>
> ****
>
> List-Archive:****
>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ****
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ****
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
> ****
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ****
>
> Options & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ****
>
> ****
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ****
>
> List rules & etiquette:****
>
> ****
>
> www.re-wrenches.org/etiquette.htm****
>
> ****
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> ****
>
> ****
>
> ****
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
> for the use of the individual or entity who is the intended recipient and
> may contain information that is privileged, confidential and exempt from
> disclosure or any type of use under applicable law. If the reader of this
> e-mail is not the intended recipient, or the employee, agent, or
> representative responsible for delivering the e-mail to the intended
> recipient, you are hereby notified that any dissemination, distribution,
> copying, or other use of this e-mail is strictly prohibited. If you have
> received this e-mail in error, please reply immediately to the sender. ***
> *
>
> *P* Please think of the environment before printing this email****
>
>
>
>
> ****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
> ** **
>
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ** **
>
> Options & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ** **
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ** **
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ** **
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> ** **
>
> ** **
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
> for the use of the individual or entity who is the intended recipient and
> may contain information that is privileged, confidential and exempt from
> disclosure or any type of use under applicable law. If the reader of this
> e-mail is not the intended recipient, or the employee, agent, or
> representative responsible for delivering the e-mail to the intended
> recipient, you are hereby notified that any dissemination, distribution,
> copying, or other use of this e-mail is strictly prohibited. If you have
> received this e-mail in error, please reply immediately to the sender.
>
> *P* Please think of the environment before printing this email
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130117/4c6ecae7/attachment-0001.htm>
More information about the RE-Wrenches
mailing list