Or often science

Jay

Peltz power

Sent from my iPad

On Jan 16, 2013, at 6:50 AM, Drake <drake.chamberlin at redwoodalliance.org> wrote:

> That is an interesting point.  The Code issue is one of definition, not of function or safety. 
> 
> At 04:02 PM 1/15/2013, you wrote:
>> Hi August,
>> 
>> I maintain that the WEEB is an irreversible splice.
>> If you want to disconnect a WEEB from a structure, you must irreversibly damage the device. It cannot be reused.
>> 
>> Admittedly the force required to remove a WEEB is less than that required for a thermal splice, but it doesn't take much force to just cut a wire either.
>> 
>> I would argue that the intent of the code is to prevent inadvertent removal of the ground. You must knowingly remove a WEEB from the grounding path and if you do so in the maintenance of an array, good workmanship requires that you restore the connection. 
>> 
>> Best Regards,
>> Brian 
>>> 
>>> 
> 


More information about the RE-Wrenches mailing list