[RE-wrenches] Xantrex 6048 installation for house with existing automatic generator design assistance

Chris Mason cometenergysystems at gmail.com
Mon Dec 30 17:45:24 EST 2013


A house with 2 x 400A panels draws a maximum of 20A? There's something
wrong in your numbers.


On Mon, Dec 30, 2013 at 5:45 PM, Christopher Warfel <
cwarfel at entech-engineering.com> wrote:

> I am working on a project that requires someone with more experience than
> I have in generators and transfer switches.
>
> Would you please contact me off line if interested
>
> Currently
>
> Utility fed house with two 400 amp panels.  Maximum total house current
> drawn over a long monitoring period is 20 amps. Owner wanted these panels
> so almost every load is on its own breaker.
>
> The house also has a 25kVa generator on an automatic transfer switch.
>
>
>
> Proposed
>
> Installing two 3.2kW arrays each on its own Xantrex 80amp600Vdc charge
> controller.
>
> Battery backup system to take through momentaries and short duration (1
> day? outages)
>
> Want to use existing generator to charge batteries and power house in the
> event of utility outage, and batteries are at low voltage state.
>
> Required to automatically revert to Current situation if inverter fails
> and no one is home. [This is the part that I need assistance on]
>
> Thank you, Chris
>
>
>
>
>
> --
>
> Christopher Warfel, P.E.
> ENTECH Engineering, Inc.
> Energy Utilization Experts
> (401)466-8978
>
> The information contained within this communication shall
> be considered confidential and shall not be retransmitted
> without knowledge of the sender. Please contact us if
> this email reached you in error. Thank you.
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131230/bdabf91a/attachment.htm>


More information about the RE-Wrenches mailing list