[RE-wrenches] Sick pack
frenergy
frenergy at psln.com
Thu Dec 19 01:28:52 EST 2013
Gentlemen and women,
I have been called in to deal with a pack of 16 (4 strings of 4 for 24V), L-16s, 6 years old. She is having to run her generator 2 times a day. Here in N.E. CA. its been cold, mostly clear, little wind. Her inputs are about 1 KW of PV, and small wind machine and of course a serious generator. Cables and terminals looked clean, were tight. The bulk setting on the Trace 4024 was 28.0 V for 2 hrs with RTS, however, she would manually turn off the generator soon after it reached 28V. Recipe for suphation.
Rather than getting into too much detail, here's my quandary. When I fired up the generator, the input amps in each of the 4 strings were.... string #1:29A, 2:34 A, 3:25 A, 4: 13 A. A survey of IR temps throughout the pack gave temps ranging from 63 to 92 degrees. The highest temps were in the string pulling highest amps. In trying to find shorted/failed and/or sulphated cells which data are most relevant? Temps, amp draw during charge, disconnect strings from each other and check volts of each 6 volt batt?, active bubbling? ...all the above?
I'm thinking I should have (1) checked the amp draw with batts under load/genny off in each string AND (2) check amps between strings with the pack at rest, no input or output. I would love to EQ the pack but with a temp already in the 90's and uneven currents in the strings I don't want to risk too high of temp or worse, a runaway situation and fire. I'm thinking I'd like to yank a few bad batts and run on 3 strings and then carefully EQ.
I appreciate any insights.
Thanks in advance,
Bill
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131218/ba32f8b4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: FRS_working_logo.jpg
Type: image/jpeg
Size: 42037 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131218/ba32f8b4/attachment.jpg>
More information about the RE-Wrenches
mailing list