[RE-wrenches] Adding Charge Controller(s)

jay peltz jay at asis.com
Thu Oct 24 16:26:52 EDT 2013


Hi Jeffe,

I don't know the specs on those Kyocera, but if they are the same VOC then they are fine together.

As to a enclosure for the CC's, I'd look at Midnight.
They have about a million different boxes, you'll find one that will do the job for you I'm sure.

Depending on the area, you might look at a midnight 150v, or  200v or 250v controller, as you can then run all in series.

jay

peltz power


On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote:

> Hello,
> 
> Looked at a system today that consisted of the following:
> 
> 15 - Kyocera 158W modules
> 3 -   Kyocera 185W modules
> 1 -   Outback MX60
> 8 -   New Trojan L16RE (48V system)
> 1 -   Xantrex SW Plus 
> 
> 6 months ago he swapped out his old charge controller to the new MX60 and purchased the new batteries at that time.  The array wiring did not change and is wired in 6 strings of 3.  (confusing to the MX60?)
> 
> He is now adding 4 Kyocera 240W modules.  He also purchased another MX60 for this array.
> 
> From my perspective, removing the 3 185W modules and getting them on their own controller would be a better use of the modules.  The system currently does not have any disconnects on the PV side.  There are fuses in the combiner boxes on the array, but no disconnects inside at the charge controller.  So adding 3 charge controllers, and now needing to add GFDI, means a box of some kind needs to be added to house these breakers. 
> 
> Outbacks GFPs and panel mount breakers will work, but what is the best mounting solution for these?  One DC Flexware enclosure? It will of course allow for all the DC OCPD  and allow for the landing of the output of the charge controllers.  Or is there another enclosure/OCPD solution I should look at?  
> 
> 
> Thanks as always!
> 
> Jesse
> 
> 
> 
> 
> 



More information about the RE-Wrenches mailing list