Don wrote -
"Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240
3-phase with a hi-leg (stinger)?"
Well I don't know about other brands, but can guarantee that the SMA 10TL
doesn't work on a 240 Delta with high leg, because we got burned by that.
Had to change two of them out for Fronius 10's, which worked fine.
As far as I could tell, this limitation on the SMA TL is not documented
anywhere on the manual or data sheet.