[RE-wrenches] Trace SWs in Energy Management Mode

William Miller william at millersolar.com
Fri Oct 4 17:28:14 EDT 2013


Brian:

 

Indeed LBX can have the unintended consequence of charging during peak hours
if the loads draw the batteries down during that time.  This can be avoided
if you can control the loads so all or most do not operate during peak
hours.

 

William

 

PS:  The obvious logic is that if you can control the loads to operate
minimally or not at all during peak hours, you don't need inverters and
batteries anyway.

 

Wm

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Friday, October 04, 2013 1:39 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trace SWs in Energy Management Mode

 

Thanks, I was thinking about using LBX, but the customer is really not too
excited about it.  And based on the manual, Energy Management Mode seems
like it fits the bill, but it doesn't seem to be going back into
stand-alone/inverter mode when the timer is supossed to turn off.




 

Brian Mehalic 
NABCEP Certified Solar PV Installation ProfessionalT R031508-59

IREC ISPQ Certified Affiliated Instructor/PV US-0132

 

PV Curriculum Developer and Instructor

Solar Energy International
http://www.solarenergy.org

 

On Fri, Oct 4, 2013 at 3:42 PM, <Eric.Bentsen at schneider-electric.com> wrote:


Hi Brian, 
LBX would be better for the way this customer is using the system, because
it only connects 
 to the grid when the batteries get low. Unfortunately, the timers do not
affect LBX, so charging 
may occur during the peak rate....or it may not :C) 

Rgds, 