Thanks, I was thinking about using LBX, but the customer is really not too
excited about it. And based on the manual, Energy Management Mode seems
like it fits the bill, but it doesn't seem to be going back into
stand-alone/inverter mode when the timer is supossed to turn off.
Brian Mehalic
NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132
PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org
On Fri, Oct 4, 2013 at 3:42 PM, <Eric.Bentsen at schneider-electric.com> wrote:
>
> Hi Brian,
> LBX would be better for the way this customer is using the system, because
> it only connects
> to the grid when the batteries get low. Unfortunately, the timers do not
> affect LBX, so charging
> may occur during the peak rate....or it may not :C)
>
> Rgds,
>
>
> _____________________________________________________________________________________
> *
> Eric Bentsen* | * Schneider Electric ** | Solar Business* | *UNITED
> STATES* | *Technical Support Representative* *
> Phone:* +(650) 351-8237 ext. 001# | *
> Email:* *eric.bentsen at schneider-electric.com*<eric.bentsen at schneider-electric.com> |
> *Site:** www.schneider-electric.com/solar*<http://www.schneider-electric.com/solar> |
> *Address:* 250 South Vasco Rd., Livermore, CA 94551
> *
> * <http://www.schneider-electric.com/solar>
> *** Please consider the environment before printing this e-mail
>
>
>
> From: Brian Mehalic <brian at solarenergy.org> To: RE-wrenches <
> re-wrenches at lists.re-wrenches.org> Date: 10/04/2013 12:04 PM Subject: [RE-wrenches]
> Trace SWs in Energy Management Mode Sent by:
> re-wrenches-bounces at lists.re-wrenches.org
> ------------------------------
>
>
>
> Have a friend that is on an electric co-op where peak $/kWh is 4x the
> off-peak rate. Peak hours are 6-10 am in the winter and 12-6 pm in the
> summer.
>
> He has relocated an older system from his previous house to his new one;
> circuits were separated out to sub-panel that is connected to the inverter
> AC output. The reinstallation is very professional.
>
> Two Trace SW4024 in series (04/96)
> 120/240 Vac Grid connected to AC1 of each inverter
> 575 Ah battery bank
> Two C40s with digital displays, ~ 4.5 kW STC array total
> Trimetric
>
> The goal is to not use any utility energy during peak times, unless the
> low battery voltage setting is reached, and in general to run as an
> off-grid system, minimizing charge time from the grid during off-peak hours
> as well. The assumption (I know it's a tough one, but I'm coming in after
> the transition) is that the PV array should at least be able to provide the
> bulk of the load; using the grid to charge the batteries to ensure they are
> regularly filled and to maximize their life expectancy. The customer is
> also managing loads actively.
>
> It's been a few years, but I used to work on these all the time; however
> it was usually off-grid with a genset, or fixing poorly maintained Y2K
> systems which were always in float. I'm attempting to use the energy
> management mode.
>
> Inverter settings:
> Clocks: Time is accurate
> Grid AC1 amps AC: 60
> Max charge amps AC: 10 (each inverter)
>
> Grid usage: FLT
> Set start charge time: 23:00
> Start bulk time: 23:10
> Set end charge time: 05:00
> Set float volts DC: 25.4
> Bulk volts DC: 28.8
> Absorb time: 1.5 hours
> Low battery cut-out: 22
> Low battery cut-in: 25.4
>
> Okay, programmed the system, both inverters are inverting, AC1 is blinking
> green, looks good. Then a well pump kicks on, registers 70 A DC on the
> Trimetric. This causes inverter 1 to go into bulk charging and pass
> through about 10 additional amps from the grid to the load (inverter 2
> continued to inverter about 10 amps for the load). Inverter 1 soon cycled
> into float, then went back to what invertering (amber light) and green
> blinking AC1 (which is what I want it to be at).
>
> Had to leave, both the customer and I had other obligations.
>
> He took a picture of the inverter sat 11:15 pm, and they were in bulk,
> battery voltage rising...exactly as planned. But then in the next set of
> pictures, taken at 7 am, after the end of the charge time, they were in
> float, not inverting, even though, based on the Trimetric readings at 11
> (64%, 85A charging), and the fact that charging would have been active all
> night, they were not in anyway at a low voltage condition (Trimetric
> readings am readings were 85%, trickle charge, 25.6 V).
>
> Something seems amiss. Any suggestions or insight?
>
> Thanks!
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>
> PV Curriculum Developer and Instructor
> Solar Energy International*
> **http://www.solarenergy.org* <http://www.solarenergy.org/>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
> _______________________________________________
>
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131004/c800861f/attachment.htm>
More information about the RE-Wrenches
mailing list