[RE-wrenches] Generator automatic disconnect
Ray Walters
ray at solarray.com
Wed Oct 2 00:10:48 EDT 2013
If they HAD to have the wee Generac, you could have it feed only one
inverter, and the other 3 Magnums could stay in invert mode. I have
large systems where I'm not using the charger off every inverter.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 10/1/2013 11:09 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
> You are right. Normally I would not even consider a generator of this
> size. My constant thinking outside the box took me down this rabbit
> trail. I'm back.
>
> Thank you,
>
> Larry
>
>
>
>
> On Oct 1, 2013, at 8:24 AM, Allan Sindelar
> <allan at positiveenergysolar.com <mailto:allan at positiveenergysolar.com>>
> wrote:
>
> Agreed. We're all offering ways to work as well as possible with the
> wrong generator choice for this application.
> Allan
>
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder, *Positive Energy, Inc.*
>
> A Certified B Corporation^TM
> 3209 Richards Lane
> Santa Fe, New Mexico 87507
> *505 424-1112 office 780-2738 cell*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
>
> On 10/1/2013 9:16 AM, Ray Walters wrote:
>> Sounds like they need a 20 Kw Kohler. Hot Tub in the future? They'll
>> love their Kohler. The Generac is just way too small to even
>> consider IMHO.
>>
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>>
>> On 10/1/2013 8:11 AM, Larry Crutcher, Starlight Solar Power Systems
>> wrote:
>>> William, Chris, Ray, Allan, et al.
>>>
>>> Gen support would be ideal but this inverter setup will be a quad
>>> pack of Magnum 4024PAE (120/240 split; 16kW). Their New MSH inverter
>>> is single phase only and can not be stacked.
>>>
>>> While disabling load(s) is the antithesis of the desired outcome,
>>> I'll review this possibility further.
>>>
>>> Using a separate charger could work but it would need to be about
>>> 200A @ 32V which would add quite a bit of cost and be hard to sell
>>> since the Magnum inverters already have 4 high quality charges
>>> included.
>>>
>>> A larger generator might be necessary if the customer won't agree to
>>> load shedding. Their plans are to expand the loads over time,
>>> operate a business, install a hot tube and more. Of course I have
>>> pushed the concept that conservation is paramount. The PV array and
>>> inverters are being oversized now for the future growth.
>>>
>>> My ideal solution...Since Magnum inverters monitor the AC input and
>>> control it based on quality of power, it seems to me that there
>>> could be a setting for disconnecting the AC input if loads exceed a
>>> setpoint. Change in control software would be great.
>>> Thank you,
>>> Larry
> _______________________________________________
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20131001/a9181d3a/attachment.htm>
More information about the RE-Wrenches
mailing list