[RE-wrenches] Utilities see battery bank as parasitic load?
toddcory at finestplanet.com
toddcory at finestplanet.com
Tue Sep 24 18:48:58 EDT 2013
"As SCE wrote in a July memo for solar and storage contractors ([https://www.sce.com/wps/wcm/connect/7bfb9fcc-b277-4646-9ac2-7700e03914bf/Battery_Backed_Storage_NEM_Eligibility.pdf?MOD=AJPERES] PDF), “if a renewable generator is modified so that the battery storage system is integrated into the generator, SCE cannot separately meter the energy from the renewable PV generator and the non-renewable battery.”
this is bullshit!
most all of the grid-tie systems i do here (in unreilable norcal power area) incorporate battery backup... and they are all metered with kv2c meters which accurately detail power generated by the system AND battery consumption... usually around 5 kWh a year.
sigh!
todd
On Tuesday, September 24, 2013 3:37pm, "Chris Daum" <chris at OasisMontana.com> said:
Allan: I know, THAT is a major concern of mine. Is anyone else having this problem?
I'd hoped there would, by now be a national/federal "agreement" on what constitutes a save battery based grid-tie system, but I guess we're not there yet....
--Chris @ the Oasis MT
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Tuesday, September 24, 2013 4:20 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Utilities see battery bank as parasitic load?
Chris,
This issue is being covered in the RE media quite actively, as threats to industry success such as these can set precedents in other states.
Check out [http://www.greentechmedia.com/articles/read/fight-over-battery-backed-solar-in-southern-california?utm_source=Solar&utm_medium=Picture&utm_campaign=GTMDaily] http://www.greentechmedia.com/articles/read/fight-over-battery-backed-solar-in-southern-california?utm_source=Solar&utm_medium=Picture&utm_campaign=GTMDaily. That's from this week.
Allan
Brian:
The LADWP engineer (Tony Ramirez) advised the inspector (Brenden Owens) who told my customer (who, ironically, is retired from working at LADWP) that he couldn't have a straight battery-based system. And has to interface his system with a batteryless grid-tie inverter.
You know any of these guys? Got any clout with them?
--Chris Daum
Oasis Montana Inc.
From: [mailto:re-wrenches-bounces at lists.re-wrenches.org] re-wrenches-bounces at lists.re-wrenches.org [[mailto:re-wrenches-bounces at lists.re-wrenches.org] mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Brian Teitelbaum
Sent: Tuesday, September 24, 2013 2:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Utilities see battery bank as parasitic load?
Chris,
Is that the “inspector” saying that, or the LADWP rep?
Brian Teitelbaum
AEE Solar
From: [mailto:re-wrenches-bounces at lists.re-wrenches.org] re-wrenches-bounces at lists.re-wrenches.org [[mailto:re-wrenches-bounces at lists.re-wrenches.org] mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Daum
Sent: Tuesday, September 24, 2013 12:41 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Utilities see battery bank as parasitic load?
Hello Wrenches:
Ok, here's one for you. We have a customer whose utility provider is L.A. Dept. of Water & Power; he's getting ready to install his battery-based grid-tie system with a Radian inverter, load center, HUB4, eight - 250W modules....etc. But the inspector is calling foul, saying his 'battery bank is a parasitic load" -- the inspector also claims that the battery bank is a “generator” so he must utilize a straight grid-tie inverter (5KW Power One) and make this an AC coupled system to be legal.
The question then becomes; does the PowerOne GT5kW inverter play nicely with the Outback Radian when the Radian is the BB Inverter?
Maybe there is a way to save our customer the cost of the new PowerOne inverter if we configure the Radian differently?
Any advice or suggestions that you can offer would be most helpful! And is anyone else running into this? It just seems crazy.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
_______________________________________________List sponsored by Home Power magazineList Address: [mailto:RE-wrenches at lists.re-wrenches.org] RE-wrenches at lists.re-wrenches.orgChange email address & settings:[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:[http://www.re-wrenches.org/etiquette.htm] www.re-wrenches.org/etiquette.htmCheck out participant bios:[http://www.members.re-wrenches.org] www.members.re-wrenches.org
Sent from Finest Planet WebMail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130924/5650408e/attachment.htm>
More information about the RE-Wrenches
mailing list