[RE-wrenches] transformerless inverters and conductor colors
Jesse Dahl
dahlsolar at gmail.com
Tue Sep 24 00:12:19 EDT 2013
Marco,
You said that after your "j-box" you will transition to THHN/THWN. Wouldn't you still need to use PVWire or some type of jacketed cable all the way to the inverter?
Jesse
Sent from my iPhone
On Sep 23, 2013, at 4:09 PM, Brian Mehalic <brian at solarenergy.org> wrote:
> The 2014 NEC addresses this in a change in 215.12(C)(2), "Feeders Supplies from Direct-Current Systems". (There is similar language in 210.5(C)(2) in regards to branch circuits). I know many folks won't be on the 2014 cycle for some time, but at least it is defined now.
>
> Conductors 6 AWG or smaller have to be identified by polarity at all termination, connection, and splice points as in one of 3 ways:
>
> Ungrounded, positive polarity
> 1: red
> 2: red stripe along entire length (conductor cannot be white, gray, black or green)
> 3: "+", "POS", or "POSITIVE" marked at least every 24 inches (again conductor cannot be white, gray, black or green)
>
> Ungrounded, negative polarity
> 1: black
> 2: black stripe along entire length (conductor cannot be white, gray, red or green)
> 3: "-", "NEG", or "NEGATIVE" marked at least every 24 inches (again conductor cannot be white, gray, red or green)
>
> Additionally, the methods used must be documented and "readily available or...permanently posted" at the equipment.
>
> Cheers,
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional™ R031508-59
> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>
> PV Curriculum Developer and Instructor
> Solar Energy International
> http://www.solarenergy.org
>
>
> On Mon, Sep 23, 2013 at 3:59 PM, Ray Walters <ray at solarray.com> wrote:
>> Hi Marco;
>>
>> Article 200.7 specifically prohibits using white wire for anything but grounded conductors. This came up last year on a large project with an ungrounded array, that also had white incorrectly specified in the plans. The appropriate colors would be red for positive, and black for negative.
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 9/23/2013 1:27 PM, Marco Mangelsdorf wrote:
>>> Hi all,
>>>
>>>
>>>
>>> We’re doing more and more installs with TL inverters (SMA and P1).
>>>
>>>
>>>
>>> I’m using double-insulated wire from the array string to the first enclosure, as in j-box, and then transitioning to standard THHN/THWN wire.
>>>
>>>
>>>
>>> I recently purchased some of that #10 double-insulated wire, getting a spool of black and white.
>>>
>>>
>>>
>>> Then after receiving the two spools it occurred to me: since the array is ungrounded, as far as there being no grounded conductor in the circuit, did I blow it by getting a spool of white wire?
>>>
>>>
>>>
>>> What sayeth you all? Can I not use that white wire in those array circuits for TL inverters?
>>>
>>>
>>>
>>> Thanks,
>>>
>>> marco
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130923/61425a95/attachment.htm>
More information about the RE-Wrenches
mailing list