[RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters

Nick Soleil nsoleil at enphaseenergy.com
Wed Sep 18 13:19:27 EDT 2013


Hi Bill and wrenches,

To clarify, our new Enphase M250 microinverter does not have a grounding
terminal.  The grounding of the M250 will be provided through the Engage
cable.  We only have a hole in the lid, in the rare case that a lug will be
desired or required by the AHJ, but we do not provide the grounding clip
with the microinverter.  A grounding terminal can be added to the
microinverter.  We have an application note on alternate grounding methods
for the M250, if needed.


On Wed, Sep 18, 2013 at 9:37 AM, Bill Brooks <billbrooks7 at yahoo.com> wrote:

> Dave, Gary, and Charlie,****
>
> ** **
>
> First, the directions from the manufacturer should be the guide as to
> whether a GEC is required or not. Just because a GEC terminal is located on
> the equipment, does not mean that one is required. Case in point—Enphase’s
> new IG product does not require a GEC, yet it has a grounding terminal for
> AHJs that might insist on one. This terminal  is not intended for a GEC,
> but it is intended for an extra EGC if the AHJ requires it (LOL on all the
> abbreviations). ****
>
> ** **
>
> The 2014 NEC makes it very clear that ungrounded PV systems do NOT require
> an GEC on the dc side and that the ac EGC is sufficient to provide a ground
> reference for the required dc EGC.****
>
> ** **
>
> “690.47(B) *Direct-Current Systems.* …*An ac equipment grounding system
> shall be permitted to be used for equipment grounding of inverters and
> other equipment and for the ground-fault detection reference for ungrounded
> PV systems.*****
>
> ** **
>
> “690.47(C)(3) *Combined Direct-Current Grounding Electrode Conductor and
> Alternating-Current Equipment*
>
> *Grounding Conductor.** An unspliced, or irreversibly spliced, combined
> grounding conductor shall be run from*
>
> *the marked dc grounding electrode conductor connection point along with
> the ac circuit conductors to the grounding*
>
> *busbar in the associated ac equipment. This combined grounding conductor
> shall be the larger of the sizes specified*
>
> *by 250.122 or 250.166 and shall be installed in accordance with
> 250.64(E).* *For ungrounded systems, this conductor shall be sized in
> accordance with 250.122 and shall not be required to be larger than the
> largest ungrounded phase conductor.**”*
>
> * *
>
> Red letters not Jesus’ words. This is the new language of the 2014 NEC. It
> is now in print.****
>
> ** **
>
> The very practical reason that a 6AWG is only required with a single
> ground rod has to do with the current carrying capacity of a 5/8”, 8’
> ground rod in soils of low resistivity—nothing more.****
>
> ** **
>
> Bill.****
>
> ** **
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Dave Click
> *Sent:* Wednesday, September 18, 2013 5:38 AM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV
> system with microinverters****
>
> ** **
>
> I think Gary may be overthinking this. If the micro-inverters have a GEC
> lug then you'll need to run a GEC.
>
>
> If you run your GEC to a ground rod, then you don't need to use one larger
> than #6 per 250.166(C). (note also (D) and (E) but they're less useful to
> you here)
> *
> Commentary:*
> It makes no sense to me why the NEC can require a 0.9in diameter, #600mcm
> GEC for some systems (not this one) per 250.166(B) and then say "oh wait,
> you installed a single ground rod? Then a #6 is all you need!" in
> 250.166(C). But it certainly makes our lives easier.
>
> If the building GE is not a ground rod, you could still run your #6 GEC to
> that new ground rod, and then bond that rod to the existing electrode using
> whatever size jumper is required per 250.53 (which I believe would also be
> a #6). This lets you keep that 300' run as a #6 rather than a #4 or #2 that
> may be required otherwise.
>
> DKC****
>
> On 2013/9/17 23:56, Gary Willett wrote:****
>
> Charlie:
>
> The answer depends on whether the "system" (modules and micro-inverters)
> is "grounded" or "ungrounded". I think you are describing a "grounded"
> system, but it's not totally clear based on your issue description.
>
> If the micro-inverter is "transformer-less" the conductors are not
> isolated between the DC-in and the AC-out. This requires the micro-inverter
> to have no DC-side system ground. The micro-inverter AC-side always
> requires an EGC.
>
> I am assuming that the PV modules are in close proximity to the
> micro-inverters, and the 300' home-run is for the AC outputs of the
> micro-inverters.
>
> Is either DC bus (PV+ or PV-) a grounded conductor, or are both busses
> ungrounded? If the DC-side combiners and re-combiners have OCPDs and
> disconnecting means for both PV+ and PV-, then your system is considered to
> be "floating" or "ungrounded".
>
> If the system is "ungrounded", a GEC is not required on the DC-side of the
> micro-inverter, and only an AC-EGC sized per NEC 690.45 is required.
>
> If the DC-side combiners and re-combiners have OCPDs and disconnecting
> means for only one conductor (PV+ or PV-), then your PV system is
> considered to be "grounded". If the system is "grounded", the combined
> DC-GEC and AC-EGC sizing requirements in NEC 690.47(C)(3) apply. The larger
> of the EGC (Table 250.122) and GEC [250.166(B)] sizes will be required.
>
> More specifics on the PV module Vmpp and micro-inverter you're dealing
> with would be helpful.
>
> Regards,
>
> Gary Willett
> Icarus Solar
>
>
> On 9/17/13 8:37 PM, Aladdin Solar wrote:****
>
> We will be installing a 40KW grid-tied PV system that uses PV modules
> wired in parallel as per the module manufacturer -- so it's a high
> amperage, low voltage system on the DC side. 2 branches of about 3KW of
> parallel wired modules each come together onto a DC bus. The DC branch
> conductors are sized as 2AWG.****
>
>  ****
>
> The inverter system provided by the manufacturer consists of a number of
> UL1741 single phase microinverters that all are powered off of the low
> voltage DC bus. So there's a bunch of microinverters in parallel, combined
> output is single phase power.****
>
>  ****
>
> Those microinverters have a ground lug labeled "GEC". You know where this
> is going...****
>
>  ****
>
> Assuming we are following NEC 690.47(C)(3), we'll be treating this ground
> as GEC and following all the GEC rules. My understanding is that because
> the DC conductors within the array are 2AWG (NEC 250.166(B), we will need
> to connect all 12 branches and 6 DC buses with continuous 2AWG and bring it
> all the way back 300' to where the AC GEC bond is located. We're getting a
> lot of pushback from the electrical sub and even some disagreement from the
> module manufacturer on this--no one's ever seen a grounding conductor of
> this size being required for this application.****
>
>  ****
>
> Please don't get too bogged down with understanding the low voltage,
> parallel module spec and the massive number of microinverters involved.
> What I'm looking for is confirmation that I am properly understanding how
> the NEC GEC requirements apply, especially to the GEC size.****
>
>  ****
>
> Charlie Pickard
> NABCEP Certified PV Installation Professional ™
> Aladdin Solar, LLC****
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 8813 (20130917) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> ****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
> ** **
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ** **
>
> Change email address & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ** **
>
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ** **
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ** **
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> ** **
>
>
>
>
>
> ****
>
> _______________________________________________****
>
> List sponsored by Home Power magazine****
>
> ** **
>
> List Address: RE-wrenches at lists.re-wrenches.org****
>
> ** **
>
> Change email address & settings:****
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org****
>
> ** **
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org****
>
> ** **
>
> List rules & etiquette:****
>
> www.re-wrenches.org/etiquette.htm****
>
> ** **
>
> Check out participant bios:****
>
> www.members.re-wrenches.org****
>
> ** **
>
> ** **
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

*
*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsoleil at enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130918/44d69a33/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1981 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130918/44d69a33/attachment.jpg>


More information about the RE-Wrenches mailing list