[RE-wrenches] Outback AC coupling Sunpower?

Ryan ryan at kb1uas.com
Wed Jul 31 14:16:03 EDT 2013


Ray
You did not mention the XW, it frequency dithers so it is a pretty 
straight forward setup. It also comes in 4, 4.5 and 6KW

Ryan


On 7/31/2013 2:04 PM, Ray Walters wrote:
> Hi Kelly;
>
> I agree the Radian system is appealing.  Its basically uses a circuit 
> breaker that can be controlled like a relay as well, and just 
> disconnects the GT inverter.
> I'm going to offer a brief table of what I've found for my choices:
>
> Brand
> 	Control Method
> 	Pros
> 	Cons
> SMA Sunny Island
> 	Frequency shift to disconnect GT inverter
> 	simplest wiring, Trusted GT industry player
> 	most expensive, Freq shift can cause other problems
> Outback Radian
> 	Remote controlled Circuit breaker disconnects GT inverter
> 	fairly simple wiring,  relay and breaker are combined, better control 
> of battery charging
> 	still expensive, not available in smaller than 8 kw model
> Magnum
> 	Diversion load controls for battery regulation  (soon to offer AC 
> load control)
> 	lower cost, proven technology, freq shift control offered as fail safe
> 	most complicated wiring,  diversion loads not always reliable or 
> available
> Modsine Backup system
> 	no AC coupling, just an old fashioned backup system
> 	low cost
> 	complicated, needs customer interaction, not as efficient, GT PV not 
> used, dedicated PV modules only charge backup system
> Generator
> 	No AC coupling, generator runs backup loads
> 	lowest cost,  backup power available for as long as outage (no batteries)
> best for week long outages that only occur every few years
> 	Not Renewable, fuel storage issues, doesn't switch fast enough to 
> maintain computers, etc.
>
>
>
> I'm still pricing out the options, but the SI and Radian seem a bit 
> overkill for smaller systems.  Backup inverter power of just a couple 
> thousand watts is all that most people need.  The Magnum is 
> appealing,  but I have quite a bit of experience with load diversion 
> controls from  wind and Hydro systems, and I really feel that its 
> overly complicated for the less than 1% of the time that the grid is 
> out.  Keeping the battery from being damaged is what's important, but 
> maintaining full 3 stage charging for a couple of days a year is not.  
> The batteries can be properly charged once the grid returns.  May be 
> able to use Outback's ROCB with the Magnum?  That might get the best 
> of both worlds.
> If I was building the entire system to start, I'd just use a single 
> Outback GVFX with its own PV array, and add GT inverters and array 
> that were independent for the rest of the GT requirements.  This 
> project however is retrofitting an existing GT system.
> I've done many backup systems in the days before Grid Tie, and they 
> work fairly well.  Basically either the modules are not used much of 
> the time, or the customer has a few circuits that are on the backup 
> system (off grid) all the time.   They operate it just like an off 
> grid system, the only difference is that when its time to run a 
> generator, they can just switch to the grid.  These are not for your 
> average customer, but can work well for someone that likes to save 
> money and tinker.
> Another consideration is that if the battery bank is large enough 
> relative to the array, over charging becomes less of an issue; 
> especially with flooded cells that can stand a bit of over charging 
> ("equalization") every now and then.   However, I can see that the 
> average small sealed battery bank hooked up to several KWs of PV could 
> get ruined in a day.
> I'll close with a quote from Joe Swartz in his 2012 Solar pro magazine 
> article :
>
> "AC coupling is still the Wild West of renewable energy applications"
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 7/30/2013 11:37 PM, Kelly Keilwitz, Whidbey Sun & Wind wrote:
>> Ray,
>> The battery-based inverter in an AC-coupled system should not be 
>> grid-interactive. The grid passes through the BB inverter to the 
>> grid-direct inverter(s). The BB inverter is there to create a stable 
>> grid-like signal for the grid-direct inverters when the grid is not 
>> present, and to manage the batteries. Thus, the pass-through AC 
>> capability of the BB inverters normally (there is a complicated 
>> work-around) must be able to handle all of the PV AC output, when 
>> loads are low.
>> You probably are aware, but to make it clear in this thread: the 
>> system needs to have some method to protect the batteries from 
>> overcharging, as a result of the grid-direct inverter output when the 
>> grid is down and loads can't use all the solar energy available. With 
>> the Sunny Islands it's done by a signal that reduces output from the 
>> Sunny Boys without disconnecting them. With Outback and others it's 
>> done with a installer-designed relay that disconnects the grid-direct 
>> inverter when the battery voltage gets to a set point. We haven't 
>> done an AC-coupled system with the Radian, yet. Sounds like the 
>> remote controlled breaker is Outback's approved and listed way to do 
>> it. About time.
>>
>> -Kelly
>>
>> Kelly Keilwitz, P.E.
>> Principal
>> Whidbey Sun & Wind
>> Renewable Energy Systems
>> NABCEP PV Installation Professional
>> WA Electrical Administrator
>> kelly at whidbeysunwind.com <mailto:kelly at whidbeysunwind.com>
>> PH & FAX: 360.678.7131
>>
>>
>>
>> On Jul 30, 2013, at 4:23 PM, Ray Walters <ray at solarray.com 
>> <mailto:ray at solarray.com>> wrote:
>>
>>> The Outback rep got me some good info, and I'm liking the Radian 
>>> with the Remote controlled breaker to control the GT inverter when 
>>> the grid is out.  I've heard of quite a few problems related to the 
>>> Sunny Island frequency controlled system.
>>> My question is can off grid inverters like the Magnum be AC coupled? 
>>>  I'm trying to get the price down, and still handle the 240 vac 
>>> input from the GT inverter.
>>> I penciled out the Radian and I was topping $10k before 
>>> installation.   This customer is hoping for a solution under $10k, 
>>> and closer to $5k if possible.  I think an elegant lower cost 
>>> solution for Grid tie with battery back up is in order.  A Radian Lite?
>>> For backup, it could even be mod sine, as it wouldn't be much worse 
>>> than generator power or the average UPS setup.
>>>
>>>
>>> R.Ray Walters
>>> CTO, Solarray, Inc
>>> Nabcep Certified PV Installer,
>>> Licensed Master Electrician
>>> Solar Design Engineer
>>> 303 505-8760
>>>
>>> On 7/30/2013 2:59 PM, Ray Walters wrote:
>>>> Hi All;
>>>>
>>>> I know AC coupled systems have been covered before, but I have a 
>>>> new issue:  positive grounding.  A customer with an existing 8kw 
>>>> Sunpower system wants to add backup.   He was put off by the high 
>>>> cost the Sunny Island, so I was steering him towards a single 
>>>> Outback VFX coupled to just one of his 3 inverters.  The issue is 
>>>> how will the VFX work with positive grounded inverters.  I'm 
>>>> assuming that since the two inverters will only be connected by AC, 
>>>> that the positive vs negative grounding of their separate DC 
>>>> systems will not matter.  Any experience with this particular 
>>>> scenario: Sunpower system AC coupled to an Outback?
>>>> Also, would I even need a GVFX, since the inverter would only be 
>>>> used during outages  (which might allow a generator to be used 
>>>> later as well)  A VFX should still AC couple to the GT inverter 
>>>> during an outage, right?
>>>>
>>>> Thanks as always,
>>>>
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org 
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>> Change email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130731/6b81259b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: C:\Users\Ryan\Documents\mnLogo_email.jpg
Type: image/jpeg
Size: 15101 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130731/6b81259b/attachment.jpg>


More information about the RE-Wrenches mailing list