[RE-wrenches] Trojan L-16s

Drake drake.chamberlin at redwoodalliance.org
Thu Jul 18 14:11:52 EDT 2013


Tom,

The batteries usually reach absorb voltage 
shortly after the sun hits the array. The reason 
the bank wasn't working correctly is that one 
cell was dead in one of the batteries.

I could increase the absorb time to 4.6 hours and 
the voltage to 29.6, especially since the bank 
has a new battery. That is longer and higher than 
I'd previously heard recommended. What would be 
the effect on water consumption?  How did you calculate the absorb time?

Thanks,


Drake



At 12:19 PM 7/18/2013, you wrote:
>Content-Language: en-US
>Content-Type: multipart/related;
> 
>boundary="_005_12a75c173ebd40919f701b08b4bd8fe6BLUPR05MB165namprd05pro_";
>         type="multipart/alternative"
>
>Drake
>
>I calculate 4.6 hours absorb time given the 
>solar you have here. So the charge rate at 29.3 
>is OK you could bump it to 29.6. It looks like 
>decreased capacity because of improper charge 
>parameters. You have to bring batteries to full 
>charge at least once every 10 days and the only 
>way to achieve full charge is by holding in the 
>absorb mode through the proper time 4.6 hours.
>
>With that said when looking here at this the 
>bulk time (based on where the batteries were 
>left off the previous night) bulk it typically 
>at least one or two hours. If you add this to 
>the 4.6 it’s 5.6 or 6.6 hours total charge time
 
>this will work in New Mexico or Arizona most of 
>the year but if this is in Ohio let’s say, the 
>real problem is not enough solar!
>
>It’s not the batteries! Yes you have a problem 
>now with them and it could be fixed but that’s a 
>different discussion. Call me 888-503-6772
>
>Tom Duffy
>Senior Solar Design Engineer
>Real-logo-X-195
>
>Toll Free 888-895-8179
><mailto:tom at thesolar.biz>tom at thesolar.biz
>Customer Service and Accounting 888-895-6810
>Grid tie sales 888-895-7847
>Off Grid sales 888-895-4058
>Other Product Sales 888-895-9612
>Central America Sales (Panama) 507-6-126-1253
>Shipping and Receiving 888-895-6497
>Tech Support 888-895-8179
>SKYPE:  thesolarbiz
>
>From: re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
>Sent: Wednesday, July 17, 2013 4:07 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Trojan L-16s
>
>Hi Tom,
>
>These are Trojan L-16E batteries, 370 AH.  They 
>have a 2 hour absorb cycle at around 29.3 
>V.  There is one series string of 4 batteries in 
>a small, off grid cabin that is used  3 or 4 
>days a week.  The system has 980 Watts of PV 
>with an Outback FM 60 CC and an Outback 3524 VFX inverter.
>
>I was concerned to read that John and Bob have 
>been seeing more problems with the Trojan L-16s 
>lately. They have been a standby for this type 
>of system. If they truly are not lasting as long 
>as previously, what other options do we have for 
>a reasonably priced, decent quality battery in that amp hour range?
>
>Thanks,
>
>Drake
>
>
>At 09:54 AM 7/16/2013, you wrote:
>
>Content-Language: en-US
>Content-Type: multipart/related;
> 
>boundary="_004_66ba8ba32edb46a18046d46a3a83c95cBLUPR05MB165namprd05pro_";
>          type="multipart/alternative"
>
>Hi Drake
>
>The first thing I would look at is how the 
>batteries are being charged
 Can they even be 
>charged by the present equipment? What is the 
>Bulk/Absorb voltage and time? Equally important 
>is the design of the bank
 series or 
>series/parallel and if parallel how many 
>strings. Lastly which Trojan L-16 are these?
>
>Tom Duffy
>Senior Solar Design Engineer
>Real-logo-X-195
>
>Toll Free 888-895-8179
><mailto:tom at thesolar.biz>tom at thesolar.biz
>Customer Service and Accounting 888-895-6810
>Grid tie sales 888-895-7847
>Off Grid sales 888-895-4058
>Other Product Sales 888-895-9612
>Central America Sales (Panama) 507-6-126-1253
>Shipping and Receiving 888-895-6497
>Tech Support 888-895-8179
>SKYPE:  thesolarbiz
>
>From: 
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>[ mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
>Sent: Monday, July 15, 2013 8:59 PM
>To: RE-wrenches
>Subject: [RE-wrenches] Trojan L-16s
>
>Hello Wrenches,
>
>A 1 1/2 year old bank of Trojan L-16s had a 
>battery with a dead cell. I have heard that 
>there have been some complaints about the L-16s 
>lately.  Has anyone had experiences with Trojan 
>L-16s (or the RE series), good or bad?  Are they 
>still a good choice to use in off grid systems?
>
>Thanks,
>
>Drake
>
>Drake Chamberlin
>Athens Electric LLC
>OH License 44810
>CO License 3773
>NABCEP Certified Solar PV
>740-448-7328
><http://athens-electric.com/>http://athens-electric.com/
>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>
>
>List-Archive: 
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130718/66ef30fd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1348b34.png
Type: image/png
Size: 17363 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130718/66ef30fd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1348b44.png
Type: image/png
Size: 17364 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130718/66ef30fd/attachment-0001.png>


More information about the RE-Wrenches mailing list