I think that the 230s required positive grounding, so you can't swap out
the inverter for a TL unit. These two circuits in parallel will be fine
for your MPPT, you'll have essentially the same voltages but slightly
higher current in your new second string.
DKC
On 2013/7/12 19:27, August Goers wrote:
>
> Hi Wrenches,
>
> I have a client with a small system consisting of 6 SunPower 230s and
> a SMA SB 3000. Anyway, he wants to add another 6 modules but the
> closest we can get from SunPower these days is a 245. The new six
> modules would go on a second string.
>
> Do you think that the slight difference in tracking voltage and
> current will be significant enough to justify the cost of adding or
> swapping the inverter? Here is the info for the modules:
>
> SunPower 230 WHT
>
> Vmpp 41.0 V
>
> Impp 5.61 A
>
> Voc 48.7 V
>
> Isc 5.99 A
>
> SunPower 245NE WHT
>
> Vmpp 40.5 V
>
> Impp 6.05 A
>
> Voc 48.8 V
>
> Isc 6.43 A
>
> I imagine that the tracker in the Sunny Boy will be a little off and
> perhaps the result will be that both strings will be running a few
> percent lower than they are capable of?
>
> Best, August
>
> *August Goers*
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> m: 415.559.1525
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130713/260ac07c/attachment.htm>
More information about the RE-Wrenches
mailing list