Hi Wrenches,
I have a client with a small system consisting of 6 SunPower 230s and a SMA
SB 3000. Anyway, he wants to add another 6 modules but the closest we can
get from SunPower these days is a 245. The new six modules would go on a
second string.
Do you think that the slight difference in tracking voltage and current
will be significant enough to justify the cost of adding or swapping the
inverter? Here is the info for the modules:
SunPower 230 WHT
Vmpp 41.0 V
Impp 5.61 A
Voc 48.7 V
Isc 5.99 A
SunPower 245NE WHT
Vmpp 40.5 V
Impp 6.05 A
Voc 48.8 V
Isc 6.43 A
I imagine that the tracker in the Sunny Boy will be a little off and
perhaps the result will be that both strings will be running a few percent
lower than they are capable of?