[RE-wrenches] 690.64(B) 2008 NEC
Allen Frishman
amfrish at aeonsolar.com
Wed Jun 26 06:23:16 EDT 2013
Hi Wrenchers,
I know this topic has been discussed several times but am in need of a little more clarification.
Here is the design:
- Inverter located on roof is grid connected to a ("Main Breaker" sub-panel that feeds multiple loads) via a solar breaker.
- Dedicated set of conductors feeding the Main Breaker sub-panel on the roof are protected in the basement electric room with a fused switch.
The Question:
Since the conductors between the fused switch in the basement & the sub-panel are protected on both ends do they need to comply with the 120% rule? As a reference the part that is in question is, are these conductors "capable of supplying multiple branch circuits,"?
All feedback is appreciated!
Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130626/f5356ebd/attachment.htm>