[RE-wrenches] Full sized neutral - 240 V inverter

Drake drake.chamberlin at redwoodalliance.org
Thu Jun 20 16:18:14 EDT 2013


Hi Wallace,

For services, at least, in the 2011 NEC, the neutral is still sized 
per Table 250.66 (250.24 (C) (1).

I took Allan's suggestion and called Power One tech support back. The 
neutral carries no current; it is strictly for sensing.

Drake

At 02:23 PM 6/20/2013, you wrote:
>Drake,
>
>Full sized neutrals are now required due to harmonics at least.
>
>The cost over your quote for neutral is fixed. What is the cost for 
>unknown consequences if you disregard manufacturers specs?
>
>Wallace Stahle
>Future Electric Energy Co
>P O Box 236
>Willits, CA 95490
><mailto:future at pacific.net>future at pacific.net
>CA Lic.# C10-762093
>707-459-0474
>
>
>On Jun 19, 2013, at 3:26 PM, Drake wrote:
>
>>That was my first call. They said use a full size neutral. I'm not 
>>satisfied with that answer. The combined experience and knowledge 
>>on this list far exceeds that of any tech support person.
>>
>>At 04:27 PM 6/19/2013, you wrote:
>>>Drake,
>>>Why not discuss this with Power One tech support?
>>>Allan
>>>
>>>Allan Sindelar
>>><mailto:Allan at positiveenergysolar.com>Allan at positiveenergysolar.com
>>>NABCEP Certified PV Installation Professional
>>>NABCEP Certified Technical Sales Professional
>>>New Mexico EE98J Journeyman Electrician
>>>Founder and Chief Technology Officer
>>>Positive Energy, Inc., a Certified B CorporationTM
>>>3209 Richards Lane
>>>Santa Fe, New Mexico 87507
>>>505 424-1112 office 780-2738 cell
>>><http://www.positiveenergysolar.com/>www.positiveenergysolar.com
>>>
>>>On 6/19/2013 1:55 PM, Drake wrote:
>>>>A very common cable for 100 A service conductors has 2 - #2 AL 
>>>>wires and 1 - #4 AL for the neutral;  200 A will have 2 - 4/0 AL 
>>>>wires and 1 - 2/0 for the neutral.   If I run # 2 to limit the VD 
>>>>on the run to the panel and reduce the neutral to #4, #12 copper 
>>>>phase and neutral will still connect to the inverters.  This 
>>>>would be code for a feeder to a separate structure.
>>>>
>>>>Does the Power One inverter actually have a major imbalance 
>>>>resulting in substantial neutral currents? If so, it is really a 
>>>>120 V inverter for VD calculations.
>>>>
>>>>
>>>>  03:37 PM 6/19/2013, you wrote:
>>>>>Content-Type: multipart/related;
>>>>>         boundary="----=_NextPart_000_00A6_01CE6CE9.D20EFB20"
>>>>>Content-Language: en-us
>>>>>
>>>>>Doug,
>>>>>705.95(B) allows you down size your neutral if it is used solely 
>>>>>for instrumentation and it must be sized equal to or larger than 
>>>>>the EGC but this is not the case. If Power One says a full size 
>>>>>neutral is needed than that means that it is not just a voltage 
>>>>>sensing conductor used for instrumentation and that it does carry current.
>>>>>
>>>>>I don't believe there are any exceptions in code for downsizing 
>>>>>your neutral in regards to upsizing the conductors to account 
>>>>>for voltage drop but I could be wrong.
>>>>>
>>>>>--
>>>>>John Stimac | Corvallis, OR
>>>>>Renewable Energy Associates LLC
>>>>>541-754-2001 Office/Fax
>>>>><mailto:john at renewableassociates.com>john at renewableassociates.com
>>>>>www.renewableassociates.com
>>>>><2221ada.jpg>
>>>>>
>>>>>
>>>>>
>>>>>From: 
>>>>><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>>>>>[ mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
>>>>>Sent: Wednesday, June 19, 2013 6:42
>>>>>To: 
>>>>><mailto:re-wrenches at lists.re-wrenches.org>re-wrenches at lists.re-wrenches.org
>>>>>Subject: [RE-wrenches] Full sized neutral - 240 V inverter
>>>>>
>>>>>Hello Wrenches,
>>>>>
>>>>>Power One tech support said that full sized neutrals had to be 
>>>>>run to a pair of 240 V, PVI 3.6 inverters.  We have a 180 foot 
>>>>>underground run to the service panel.
>>>>>
>>>>>Why do we need to run a full sized neutral all the way back to 
>>>>>the panel?  The wiring to the panel is oversized for voltage 
>>>>>drop.  The code allows for reduction of neutral size where 
>>>>>neutral imbalance is less than the current of a phase, which is 
>>>>>usually the case.
>>>>>
>>>>>Why does a neutral need to be installed that is the size of the 
>>>>>phase wiring where the imbalance should be negligible? Or is 
>>>>>there a lot of neutral current for some reason?  Am I missing something?
>>>>>
>>>>>Thanks
>>>>>
>>>>>Drake
>>>>>
>>>>>
>>>>>Drake Chamberlin
>>>>>Athens Electric LLC
>>>>>OH License 44810
>>>>>CO License 3773
>>>>>NABCEP Certified Solar PV Installer
>>>>>740-448-7328
>>>>><http://athens-electric.com/>http://athens-electric.com/
>>>>>
>>>>>
>>>>>_______________________________________________
>>>>>List sponsored by Home Power magazine
>>>>>
>>>>>List Address: 
>>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>>Change email address & settings:
>>>>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>>List-Archive: 
>>>>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>>List rules & etiquette:
>>>>>www.re-wrenches.org/etiquette.htm
>>>>>
>>>>>Check out participant bios:
>>>>>www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>>
>>>>_______________________________________________
>>>>List sponsored by Home Power magazine
>>>>
>>>>List Address:
>>>><mailto:RE-wrenches at lists.re-wrenches.org>
>>>>RE-wrenches at lists.re-wrenches.org
>>>>
>>>>Change email address & settings:
>>>>
>>>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>List-Archive:
>>>>
>>>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>>List rules & etiquette:
>>>>
>>>>www.re-wrenches.org/etiquette.htm
>>>>
>>>>Check out participant bios:
>>>>
>>>>www.members.re-wrenches.org
>>>>
>>>
>>>
>>>
>>>_______________________________________________
>>>List sponsored by Home Power magazine
>>>
>>>List Address: 
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Change email address & settings:
>>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive: 
>>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>List rules & etiquette:
>>>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out participant bios:
>>>www.members.re-wrenches.org
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130620/b0d63d82/attachment.htm>


More information about the RE-Wrenches mailing list