A very common cable for 100 A service conductors has 2 - #2 AL wires
and 1 - #4 AL for the neutral; 200 A will have 2 - 4/0 AL wires and
1 - 2/0 for the neutral. If I run # 2 to limit the VD on the run to
the panel and reduce the neutral to #4, #12 copper phase and neutral
will still connect to the inverters. This would be code for a feeder
to a separate structure.
Does the Power One inverter actually have a major imbalance resulting
in substantial neutral currents? If so, it is really a 120 V inverter
for VD calculations.
03:37 PM 6/19/2013, you wrote:
>Content-Type: multipart/related;
> boundary="----=_NextPart_000_00A6_01CE6CE9.D20EFB20"
>Content-Language: en-us
>
>Doug,
>705.95(B) allows you down size your neutral if it is used solely for
>instrumentation and it must be sized equal to or larger than the EGC
>but this is not the case. If Power One says a full size neutral is
>needed than that means that it is not just a voltage sensing
>conductor used for instrumentation and that it does carry current.
>
>I don't believe there are any exceptions in code for downsizing your
>neutral in regards to upsizing the conductors to account for voltage
>drop but I could be wrong.
>
>--
>John Stimac | Corvallis, OR
>Renewable Energy Associates LLC
>541-754-2001 Office/Fax
><mailto:john at renewableassociates.com>john at renewableassociates.com
>www.renewableassociates.com
>REAL_logo_black2
>
>
>
>
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
>Sent: Wednesday, June 19, 2013 6:42
>To: re-wrenches at lists.re-wrenches.org
>Subject: [RE-wrenches] Full sized neutral - 240 V inverter
>
>Hello Wrenches,
>
>Power One tech support said that full sized neutrals had to be run
>to a pair of 240 V, PVI 3.6 inverters. We have a 180 foot
>underground run to the service panel.
>
>Why do we need to run a full sized neutral all the way back to the
>panel? The wiring to the panel is oversized for voltage drop. The
>code allows for reduction of neutral size where neutral imbalance is
>less than the current of a phase, which is usually the case.
>
>Why does a neutral need to be installed that is the size of the
>phase wiring where the imbalance should be negligible? Or is there a
>lot of neutral current for some reason? Am I missing something?
>
>Thanks
>
>Drake
>
>
>Drake Chamberlin
>Athens Electric LLC
>OH License 44810
>CO License 3773
>NABCEP Certified Solar PV Installer
>740-448-7328
><http://athens-electric.com/>http://athens-electric.com/
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130619/02bb3ec7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1988cad.jpg
Type: image/jpeg
Size: 5932 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130619/02bb3ec7/attachment.jpg>
More information about the RE-Wrenches
mailing list