[RE-wrenches] 200 Amp Main Equip for 60A Solar
August Goers
august at luminalt.com
Thu Jun 13 10:02:05 EDT 2013
Jeff,
Why are you looking to do a supply side connection? If you're going with
new equipment you could go with a 225 A main panel with a 200 A main
breaker and do a load side connection.
Best, August
*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jeff Clearwater
*Sent:* Wednesday, June 12, 2013 6:10 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] 200 Amp Main Equip for 60A Solar
Hey Wrenchies,
Anybody know of a 200 Meter base with lugs rated for dual wire so we can do
a 60 Amp Supply side solar feed on a 200 Amp service?
Or does anyone know the right equip to get to ensure we can install 2 dual
lug taps on both single lugs? (a meter base with enough room for the T
lugs?)
Or better yet any integrated 200 Amp Service / Meter equipment that has an
accessible spot to tap 60 Amps for a Disconnect on the meter side of the
Main?
I have 2 SB 2500Us existing and want to add a single SB 5000TLUS - I show
rated output to be 46 Amps total and hence a 60 Amp needed.
Advice my esteemed colleagues?
Thanks,
Jeff
--
Jeff Clearwater
Village Power Design
Renewable Energy Design & Installation
Ecovillage Design Consultant
www.villagepower.com
413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130613/8174516a/attachment.htm>
More information about the RE-Wrenches
mailing list