Jeff.

Although not marketed for PV, the Eaton Cutler Hammer Ranch Panel CMBER88B200BTS has a 270 amp rating and comes with a 200 amp main breaker with space for a 70 amp secondary main breaker space(a tap between the meter and the main breaker) as well as pass through lugs and 8 more breaker spaces.  The local Platt stocks them at less than $300.  We have used them for several service upgrades and love them.

Jeff


Jeff Wongstrom
NABCEP Certified PV Installer
Licensed MT Residential Electrician
406.291.3416
thirstylakesolar.com

On Jun 13, 2013, at 6:32 AM, Dave Click wrote:

> Jeff,
> 
> This has been sent out on the list a few times but I don't remember anyone sharing their personal experiences with it:
> 
> http://solarprofessional.com/articles/products-equipment/product-launches/milbank-offers-load-tap-connector
> 
> 200+ 60 for a meter main is trickier. The $1100 (list) Schneider RC2M200S lets you do a 200A main and a 50A PV breaker (interconnecting on line side of the 200A), which may be close enough for you depending on your system details (10kWac @ 240V -> >52.1A breaker).
> 
> DKC
> 
> On 2013/6/12 21:09, Jeff Clearwater wrote:
>> Hey Wrenchies,
>> 
>> Anybody know of a 200 Meter base with lugs rated for dual wire so we can
>> do a 60 Amp Supply side solar feed on a 200 Amp service?
>> 
>> Or does anyone know the right equip to get to ensure we can install 2
>> dual lug taps on both single lugs? (a meter base with enough room for
>> the T lugs?)
>> 
>> Or better yet any integrated 200 Amp Service / Meter equipment that has
>> an accessible spot to tap 60 Amps for a Disconnect on the meter side of
>> the Main?
>> 
>> I have 2 SB 2500Us existing and want to add a single SB 5000TLUS - I
>> show rated output to be 46 Amps total and hence a 60 Amp needed.
>> 
>> Advice my esteemed colleagues?
>> 
>> Thanks,
>> 
>> Jeff
>> 
>> --
>> Jeff Clearwater
>> Village Power Design
>> Renewable Energy Design & Installation
>> Ecovillage Design Consultant
>> www.villagepower.com
>> 413-559-9763
>> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130613/d33aa2fd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: LOGO.jpg
Type: image/jpeg
Size: 5311 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130613/d33aa2fd/attachment.jpg>


More information about the RE-Wrenches mailing list