[RE-wrenches] Neutral - Ground Bond. Was- Outback wave form
Richard L Ratico
Richard.L.Ratico at VALLEY.NET
Fri Jun 7 18:49:31 EDT 2013
Allan,
I think most gennies bond the neutral to the chassis so the circuit breakers on
the gennie will trip in the event of a ground fault. If the neutrals weren't
bonded and the breakers didn't trip to clear it, there would be a shock hazard
on the chassis in the event of a fault. Not sure what you mean by suggesting to
disconnect the grounding conductor on the extension cord. If there's a ground
fault in the coffee maker, that might leave any metal parts of the appliance
energized and thus be an extreme shock hazard. Better to investigate the gennie
for a ground to neutral bond as well as the inverter BOS and rewire so the is
only one neutral to gound bond in the entire system, as required by code.
Apologies in advance if I have misunderstood your suggestion. Your posts are
invariably right on.
Dick Ratico
Solarwind Electric
Jeremy,
Outback may be right on, and it's worth checking.
Most portable gennies internally bond neutral to chassis, because they expect
that no typical homeowner will ground the chassis. (Inverter-generators are a
noteworthy exception to this.) Most inverter systems also have a neutral-ground
bond, if done to Code. Whe plugged into the gennie, there's thus an inherent
ground loop. Try disconnecting the grounding conductor on the extension cord.
Allan
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
On 6/7/2013 9:10 AM, All Solar, Inc. wrote:
I found out that the appliance will work fine from an extension cord with a
portable generator.
The appliance will not even work however when the backup gen is running and
transfering through the inverters.
Outback T.S. suggested to check the Neutral to ground bond so that is the next
step. Also tried to set the Power Save levels the same (stacked pair)
Jeremy
All Solar
----- Original Message -----
From: Exeltech
To: RE-wrenches
Sent: Wednesday, April 17, 2013 1:51 PM
Subject: Re: [RE-wrenches] Outback wave form
Wrenches,
While the addition of a capacitor may resolve issues associated with various
inverter/appliance/motor combinations, please make sure the capacitor(s) get
switched OUT of the circuit (disconnected) when the load itself is disconnected.
Failure to do so could under some circumstances cause the inverter control-loop
circuitry to go unstable, leading to unpredictable inverter operation, and
possible
damage/failure in the power system. Disconnecting the capacitor with the load
alleviate this possibility.
Regards to all...
Dan Lepinski
--- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems
<larry at starlightsolar.com> wrote:
From: Larry Crutcher, Starlight Solar Power Systems <larry at starlightsolar.com>
Subject: Re: [RE-wrenches] Outback wave form
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Wednesday, April 17, 2013, 2:09 PM
We experience issues like this from time to time. PF seems to be the culprit.
Have you measured it or looked at the waveform yet? How an inverter deals with
PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will
not work on a Magnum Energy and a few other sine wave inverters. However, it
will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope
trace of voltage/current of the Magnum inverter & Splendide washer. Upper trace
is voltage
By adding a 50uF run capacitor inline, it somewhat tames the current phase and
the sine wave so the Magnum can operate the washer.
(Special thanks to Al for the discovery and photos)
Larry Crutcher
Starlight Solar Power Systems
On Apr 16, 2013, at 9:46 AM, All Solar <allsolar at scswifi.net> wrote:
Have a client with a new coffee maker that will not run from their new dual
outback setup. Has anyone heard of this lately. We have had no problems with
appliances and sine wave inverters. What to look for?
Sent from Jeremy's IPhone. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list