Hi Allan,
The C-series behaves in the same way as if you were to connect the module
directly to the battery,
then watch a DC volt meter and disconnect/reconnect when the bulk voltage
is reached to "hold" the battery
at that level. It will hold at the bulk level for 1 hour, then transition
to float.
If left connected without disconnecting, the voltage would eventually
climb to Voc (approx 36VDC). So, while it is not
going to be as efficient as the MPPT controller in the bulk/absorption
stages, once the PWM controller transitions to float,
it will operate right about the sweet spot (Vmp). The question was making
a single 24V module work with a 24V battery.
PWM is the only way to do it, as the MPPT requires a higher PV voltage
due to the use of a buck transformer.
I will certainly pass on any recommendations for improvement to our
engineering team, and
I appreciate the feedback.
Eric Bentsen
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Allan Sindelar <allan at positiveenergysolar.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
06/04/2013 10:35 AM
Subject:
Re: [RE-wrenches] 24V charging with 60 cell modules
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Eric,
Please explain further, as what you wrote makes no sense to me. Mac didn't
indicate whether he wanted to charge a flooded battery (~29.2V) or sealed
(~28.4V). The C-series of PWM controllers has a fixed two-hour absorption,
which it only counts down once the bulk voltage is reached. If the bulk
voltage setpoint is above the MPP of the module, as it is in this case,
how can it ever reach float, as you suggest?
And further, this is spec-sheet calculation. In all but the coldest winter
weather, the Vmp of the module will be lower still as the module
temperature rises above 25ºC, and is likely to be even below the float
voltage in hot weather. And in the winter, if the battery is also cold, it
will need a higher voltage still to get fully charged.
So I'm with Bob-O on this one. You can't charge a 24V battery with a 20V
module. Please tell us how I'm wrong.
Thanks, Allan
P.S. - And while I'm on a virtual roll, please tell your engineering folks
to build a charge controller with a higher voltage input window. I don't
mean 600 volts at $1,500 or whatever it is; just higher than 150V. On a
48V system, we're stuck with series strings of three modules if we use the
lowest-cost-per-watt 60-cell modules. That means that systems have to be
designed with arrays in ~750-watt increments. Give us another 50-100V or
so of headroom, so we can design with strings in multiples of 3, 4, or 5.
Outback, are you listening too? The Midnite Classic does this for us...
Thanks.
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
On 6/4/2013 10:43 AM, Eric.Bentsen at schneider-electric.com wrote:
Hi Mac,
A PWM charge controller, such as the C35, will work in this application,
because it will
act like a switch that connects the panel to the battery. While the bulk
voltage will likely be slightly
higher than Vmp, once the controller transitions to float, which is approx
27V for most battery types,
it should allow the module to operate very close to Vmp.
Typically, MPPT controllers require a higher Vmp than the target charge
voltage.
Eric Bentsen
_____________________________________________________________________________________
Eric Bentsen | Schneider Electric | Solar Business | UNITED
STATES | Technical Support Representative
Phone: +(650) 351-8237 ext. 001# |
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Mac Lewis <maclewis1 at gmail.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date:
06/04/2013 08:05 AM
Subject:
[RE-wrenches] 24V charging with 60 cell modules
Sent by:
re-wrenches-bounces at lists.re-wrenches.org
Hello wrenches,
Is there a good method to charge 24V battery bank with single 60 cell
modules? Ideally, I'd like to charge a 24 V bank with a Kyocera
245GX-LFB. However, at NOTC the Vmp is 26.8V. Any good way to do this?
Thanks in advance.
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130604/86c4d18c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130604/86c4d18c/attachment.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11065 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130604/86c4d18c/attachment-0001.jpe>
More information about the RE-Wrenches
mailing list