[RE-wrenches] Fuse sizing in battery circuits
August Goers
august at luminalt.com
Mon Apr 15 16:20:01 EDT 2013
Hi Drake,
The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A)
applies. We have some really savvy inspectors in the Bay Area and they were
happy for us to be ungrounded since we're operating at 48 V. Yes, the
actual voltage might go above 50 V when charging but I believe it is the
nominal voltage that the code cares about.
Best,
August
*From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Drake
*Sent:* Saturday, April 13, 2013 12:14 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
Is it possible that not grounding the DC on an inverter could be code
compliant? In the past, we were always required to install grounding
electrode conductors to the DC negative, as required for grounding Direct
Current systems (250 VIII).
Maybe grounding can be eliminated in a purely AC coupled system due to the
fact that the system is not supplying premise wiring. Maybe the DC can be
considered as an integral part of the system supplying the AC.
The rules for grounding DC are stated below.
250.162 Direct current Circuits and Systems to Be Grounded
(A) Two-Wire, Direct-Current Systems. A 2-wire, dc system supplying
premises wiring and operating at greater than 50 volts but not greater than
300 volts shall be grounded.
Exception No. 1: A system equipped with a ground detector and supplying
only industrial equipment in limited areas shall not be required to be
grounded.
Exception No. 2: A rectifier-derived dc system supplied from an ac system
complying with 250.20 shall not be required to be grounded.
Exception No. 3: Direct-current fire alarm circuits having a maximum
current of 0.030 ampere as specified in Article 760, Part III, shall not be
required to be grounded.
In a Sunny Island system there is no charge control, nothing else in the DC
besides the battery and battery cables. Does not grounding the negative
really meet code requirements in the US ? Are the inverter cables not
considered to be premise wiring?
Thanks,
Drake
At 03:56 PM 4/10/2013, you wrote:
Content-Class: urn:content-classes:message
Content-Language: en-US
Content-Type: multipart/alternative;
boundary="_000_B448FC9E37458B469E77EA0BB954AD4702BD99AC6Emailbox01_"
August:
The SI can run with an ungrounded battery or a grounded battery.
With the internal breaker it is set up for a negative ground battery.
I believe the manual says ground at the battery terminal.
If you chose to go ungrounded you will need to have an OCPD in both battery
+ and battery – (all ungrounded conductors).
I am pretty sure the SI is not internally bonded to ground.
This is normal in the rest of the world.
Mine are running with an ungrounded battery and there isolation between
battery and ground.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA *(*Please note of our new
address.)*
T: 510.498.3200, X 747
M: 530.277.4894
*From:* re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
*On Behalf Of *August Goers
*Sent:* Wednesday, April 10, 2013 9:45 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
Hi All -
As a slightly separate topic, should we fuse both the positive and negative
battery lines with an SMA Sunny Island? I believe that the negative is
grounded so should not be fused but I've heard conflicting stories from
tech support.
Thanks,
August
*From:* re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
*On Behalf Of *Drake
*Sent:* Wednesday, April 10, 2013 5:52 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
boB,
SMA does recommend protecting Sunny Islands with a fuse on the battery,
even though the breakers on the units are rated for 10,000 Amps. Are the
SI breakers inferior others you have mentioned?
Thanks,
Drake
At 12:14 AM 4/10/2013, you wrote:
After 100's of thousands of inverters having been shipped in the last many
years
and thousands of inverters broken and shorting the battery terminals, there
has
never been (to our knowledge) one breaker that has not tripped.
The Midnite site lists the AIC rating of all our breakers I believe.
The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...
http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf
I guess there isn't a graph of AIC vs. voltage on their F series web page
but we remember
them showing us figures or a graph that says those breakers have an AIC of
more than
100,000 amps at 48 volts. We'll try to find that info or you may be able
to get that
from Carling.
I have, many times, directly connected these breakers across good L-16
battery strings
to demonstrate the left-hand rule to people where the 4/0 cable jumps apart
or towards each
other when very high current passes through those wires when they are near
each other.
It always trips. Never tried it at anything above a 48V battery banks IIRC.
Robin would like to mention that anyone that wants to use T-Classc
fuses.... Welcome back to the 1990's
boB
On 4/9/2013 1:23 PM, Ray Walters wrote:
Hey Bob;
Can you share that AIC vs Voltage chart?
Thanks,
R.Ray Walters
CTO, Solarray,
Inc
Nabcep Certified PV Installer,
Licensed Master
Electrician
Solar Design
Engineer
303 505-8760
On 4/9/2013 1:46 PM, boB wrote:
Those 250 amp and 175 amp breakers we have used for many many years now
have an AIC of 50,000 amps at 125 volts and if you look at the curve, at 48
volts
they are around 100,000 amps. I think that this information is on the label
of the breaker.
How many problems have you had with the Carlings or any other type of
those large breakers ?
boB
On 4/9/2013 10:40 AM, Michael Welch wrote:
If anyone would like an Acrobat version of this article, you can find it
here:
ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf
William Dorsett wrote at 07:00 AM 4/9/2013:
This topic comes up often enough that we ought to mention a yellowed
article in Home Power, (1992 Issue 27, pg 26). Christopher Freitas
wrote *Overcurrent
Protection for Battery-Powered Systems *where he describes experiments he
did back when he was with Ananda. He put a 2000 A Big Switch to initiate a
short (4/0 cable) between the terminals on a set of four golf cart
batteries (2 strings @ 12V). In series, he put in a 500A Shunt so he could
measure current passing and various fuses and breakers. “For comparison, we
decided to directly short the battery…the meter read 6960 amps peak current
(three seconds) …during each test the 4/0 cable lifted off the ground 4
inches into the air by the forces generated by the extremely high
current..” They videoed the 250 A ANN buss fuses arc and smoke; the 200A
Heinemann Series AM breakers (paralleled ones that maybe Roy mentioned)
went 3 seconds without breaking and the video showed a flash and blue
smoke.
175A ITE breaker with 42,000 AIC “simply tripped…but still allowed a peak
current of 2960 amps
200A Class T Littlefuse “opened promptly with no external signs of
stress…1920 amps peak current”
Christopher’s recommendations:
“Every AE system must have overcurrent protection able to interrupt the
maximum current available from the batteries. For most systems, the main
protection should use current limiting high AIC fuses, such as a Class T or
Class R. A disconnect switch which allows the fuse to be safely changed
should be included. A lower cost alternative is to mount the fuse in a fuse
holder without a disconnect. Although the fuse would always be electrically
hot, it normally would not be changed during the life of the system. The
fuse holder should be mounted outside the battery enclosure. Fuses should
not be bolted directly onto the battery terminal, as they are not designed
to handle the physical stresses that can occur without the protection of a
fuse holder.
Fuses which have exposed elements, such as ANN fuses, should not be used
because they are not current limiting and have only 2500 amps AIC. They
also may be a significant hazard when installed near batteries.
High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @ 65VDC)
can provide overcurrent protection for individual items. They cannot be
used to protect lower AIC breakers. This eliminates their use as a main
disconnect in most systems.
Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or the
Square-D QO (5000A @ 125 VDC) can be used in load distribution centers and
components, but must be protected by a current limiting fuse. Using low-AIC
breakers alone will not provide sufficient protection with a battery system
and may be a significant hazard during short circuit situations.”
It won’t pull up anymore on HP’s article search but probably Michael has a
copy he could post for those interested.*
*
Bill Dorsett
_______________________________________________
List sponsored by Home Power
magazine
List Address:
<RE-wrenches at lists.re-wrenches.org>
RE-wrenches at lists.re-wrenches.org
Change email address &
settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules &
etiquette:
<http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm
Check out participant
bios:
<http://www.members.re-wrenches.org>
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power
magazine
List Address:
<RE-wrenches at lists.re-wrenches.org>
RE-wrenches at lists.re-wrenches.org
Change email address &
settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules &
etiquette:
<http://www.re-wrenches.org/etiquette.htm>
www.re-wrenches.org/etiquette.htm
Check out participant
bios:
<http://www.members.re-wrenches.org>
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only
for the use of the individual or entity who is the intended recipient and
may contain information that is privileged, confidential and exempt from
disclosure or any type of use under applicable law. If the reader of this
e-mail is not the intended recipient, or the employee, agent, or
representative responsible for delivering the e-mail to the intended
recipient, you are hereby notified that any dissemination, distribution,
copying, or other use of this e-mail is strictly prohibited. If you have
received this e-mail in error, please reply immediately to the sender.
*P* Please think of the environment before printing this email
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130415/ac9c1857/attachment.htm>
More information about the RE-Wrenches
mailing list