Bill:
I have to disagree with you on this one. We can not abandoned a tried and
true practice just because some practitioners don't do it right. I don't
know how one can justify saying that encapsulating high voltage conductors
in a conduit is less safe than exposed in a flimsy basket. Consider snow
and ice and falling objects.
Too many installers entered the PV field without first acquiring the
necessary skills as journeymen or women electricians. I don't see the
benefit of rewriting the code to accommodate a lack of skills in the industry.
Respectfully,
William Miller
PS: The temperature adders always encourage us to enter the building
envelope at the first appropriate location to avoid adding
them. Thoughtful installers will do the same.
Wm
At 10:15 PM 3/25/2013, you wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_00E3_01CE29A6.37CC5110"
>Content-Language: en-us
>
>William,
>
>I would strongly disagree that conduit is tried and true on rooftops. I
>have rarely seen good conduit runs on rooftops. Most electricians have no
>clue how to work with expansion joints. Conduit on rooftops is a bad idea
>in general. Most conduit runs in big buildings are all done indoors for
>good reason. We are the crazy people doing things on the roof.
>
>The sooner we get away from conduitparticularly for long feeder runsthe
>better.
>
>In Europe they dont have problems with their rooftop wiring systems
>because everything is in tray.
>
>For those that dont allow cable tray for anything less than 1/0, just
>remember that if it isnt called cable tray, then 392 doesnt apply. The
>NEC would allow us to use treated lumber in place of cable tray. This
>makes no sense.
>
>We did some research on the origin of the 1/0 requirement, and it is
>ancient and no longer relevant. Just because it is in the code, does not
>mean it is correct. Thats why we try to fix it every three years.
>
>Bill.
>
>
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
>Sent: Monday, March 25, 2013 9:30 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Cable tray
>
>David:
>
>Of course, I understand that you are not saying we can willfully disregard
>the Code in anticipation of future clarification. I was just
>extrapolating on your idea.
>
>If we want an exception based on a predicted update in the code, we are at
>the mercy of the AHJ who may or may not be convinced. I think most AHJs
>are willing to diverge from the Code in a more strict interpretation, but
>not the reverse. Right now, as I read it, unless the leads are 1/0 or
>larger, we are forbade.
>
>I treat PV systems like rooftop AC units. The voltages and currents are
>similar, if not more severe. I don't believe you could or should run
>power to a rooftop AC unit in cable tray. Conduit is a tried and true
>practice and I recommend it.
>
>William Miller
>
>
>At 06:01 PM 3/25/2013, you wrote:
>
>Ouch. I promise I'm not advocating for anything like that. What I may be
>missing is the Code reference that says "no cable tray on roofs" or similar.
>
>There is so much room for improvement in wire management practices, that
>being able to use cable tray seems like a step forward. I understand some
>jurisdictions do not allow it, but it appears as though Code changes were
>made specifically to address this. It's boring stuff, but you can read the
>explanation of the Code changes in the ROP and ROC documents.
>
>The Code changes a lot with regards to PV system, and Article 690 is more
>fluid than other articles. Some of this is the Code trying to keep up with
>technology. In other cases the Code evolves based on new applications for
>existing products. Often it changes because some areas of the Code are
>confusing for electricians and inspectors alike. If the new Code language
>is more clear in its intent than previous versions, some inspectors are
>willing to let installers build to the most current standard.
>
>That's all I'm advocating for: Trying to understand how the minimum
>requirements outlined in Code evolve over time so that you can have a
>friendly and informed conversation with your AHJ over a donut.
>
>
>
>
>On Mar 25, 2013, at 6:26 PM, William Miller wrote:
>
>
>David:
>
>This is great news. Now, whenever I want to do something that is
>prohibited by code, I can just say that the Code Making Panel is gonna
>correct that pesky code section (insert your problem citation here) any
>day now, so I might as well be allowed to do whatever it was I was fixin'
>to do anyway. Unless I am missing something...
>
>Thanks!
>
>William Miller
>
>PS: Just kidding. Hope no offense is taken.
>
>wm
>
>
>At 03:46 PM 3/25/2013, you wrote:
>
>
>So if you ever get called on 392.10(B)(2), I think you can point out that
>the Code Making Panels have been busy clarifying that cable tray is okay
>for source circuit conductors. Unless I'm missing something....
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>Miller Solar
>Voice :805-438-5600
>email: <mailto:william at millersolar.com>william at millersolar.com
>http://millersolar.com
>License No. C-10-773985
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2013.0.2904 / Virus Database: 2641/6205 - Release Date: 03/26/13
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130326/b1510b79/attachment.htm>
More information about the RE-Wrenches
mailing list