[RE-wrenches] Cable tray
William Miller
william at millersolar.com
Tue Mar 26 00:29:40 EDT 2013
David:
Of course, I understand that you are not saying we can willfully disregard
the Code in anticipation of future clarification. I was just extrapolating
on your idea.
If we want an exception based on a predicted update in the code, we are at
the mercy of the AHJ who may or may not be convinced. I think most AHJs
are willing to diverge from the Code in a more strict interpretation, but
not the reverse. Right now, as I read it, unless the leads are 1/0 or
larger, we are forbade.
I treat PV systems like rooftop AC units. The voltages and currents are
similar, if not more severe. I don't believe you could or should run power
to a rooftop AC unit in cable tray. Conduit is a tried and true practice
and I recommend it.
William Miller
At 06:01 PM 3/25/2013, you wrote:
>Ouch. I promise I'm not advocating for anything like that. What I may be
>missing is the Code reference that says "no cable tray on roofs" or similar.
>
>There is so much room for improvement in wire management practices, that
>being able to use cable tray seems like a step forward. I understand some
>jurisdictions do not allow it, but it appears as though Code changes were
>made specifically to address this. It's boring stuff, but you can read the
>explanation of the Code changes in the ROP and ROC documents.
>
>The Code changes a lot with regards to PV system, and Article 690 is more
>fluid than other articles. Some of this is the Code trying to keep up with
>technology. In other cases the Code evolves based on new applications for
>existing products. Often it changes because some areas of the Code are
>confusing for electricians and inspectors alike. If the new Code language
>is more clear in its intent than previous versions, some inspectors are
>willing to let installers build to the most current standard.
>
>That's all I'm advocating for: Trying to understand how the minimum
>requirements outlined in Code evolve over time so that you can have a
>friendly and informed conversation with your AHJ over a donut.
>
>
>
>
>On Mar 25, 2013, at 6:26 PM, William Miller wrote:
>
>>David:
>>
>>This is great news. Now, whenever I want to do something that is
>>prohibited by code, I can just say that the Code Making Panel is gonna
>>correct that pesky code section (insert your problem citation here) any
>>day now, so I might as well be allowed to do whatever it was I was fixin'
>>to do anyway. Unless I am missing something...
>>
>>Thanks!
>>
>>William Miller
>>
>>PS: Just kidding. Hope no offense is taken.
>>
>>wm
>>
>>
>>At 03:46 PM 3/25/2013, you wrote:
>>
>>>So if you ever get called on 392.10(B)(2), I think you can point out
>>>that the Code Making Panels have been busy clarifying that cable tray is
>>>okay for source circuit conductors. Unless I'm missing something....
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130325/86a19533/attachment.htm>
More information about the RE-Wrenches
mailing list