I concur with William's recommendations and would add a couple of things.
Only use stainless steel hardware for all battery connections.
Wire brush connection surfaces prior to mating.
Use corrosion inhibiting grease on all fittings after making them (to seal out air).
Lastly, It is a good idea to use stainless Belleville washers (cupped spring washers) in current carrying connections.
Bolt head, washer, Battery terminal, washer, Belleville washer, locknut.
The spring washer maintains clamping force as the connection expands and contracts (thermally).
They are very common place in high current bus bar connections but I rarely see them used on batteries.
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Monday, March 25, 2013 12:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GSCM-mini with Honda EM5000SX
Eric:
The generator-based charging may impose higher currents into the batteries than either PV charging or inverter consumption, triggering the problem.
Melted battery terminals are not uncommon. You must have washers under your bolt heads with lead flanges. Otherwise the bolt heads sink into the lead, loosening connections. All mating surfaces need to be newly wired brushed just before assembly. Battery connections need to be re-torqued annually.
William Miller
At 09:40 AM 3/25/2013, you wrote:
Larry,
Thanks for your reply. For some reason the schematic I received from the tech at Atkinson did not show any wires being connected to pins 9 & 10 and as I'm a literalist I did not make those connections. After I received your (and other) feedback I connected gen power to those pins and the AGS seemed to function fine. Within 2 days the customer called me back saying his genny was shutting off after 20 mins of runtime. I told him to disconnect or reprogram one system component at a time to find the fault source. Before a fault source was determined, he observed that two batteries in his bank were experiencing the "battery terminals melting into the battery casing" (as was texted to me by the customer). I have no idea how a GSCM interface would cause or allow an overcurrent fault at the batteries but the timing of the installation seems to indicate that the AGS is at fault. Ever heard of this before?
Eric Stikes
SunHarvest Solar
We install solar pool pumps quite frequently here in the Caribbean. We use Sunpumps - excellent company, great support. Email Joe Lines joe at sunpumps.com<mailto:joe at sunpumps.com> for design assistance, he is very helpful.
On Wed, Feb 20, 2013 at 1:02 PM, William Korthof <wkorthof at gmail.com<mailto:wkorthof at gmail.com>> wrote:
A few questions.
I have a customer who really wants a solar-direct pool pump for his home. Medium size in-ground pool and I'd like the pump to be strong enough to lift to the solar pool panels (12 ft lift above pool level). I'd like to offer him hardware that is at least one notch above experimental beta-test. I remember the SunCentric from several years ago, but not sure how durable that turned out, and I was having trouble a vendor for it now. Any suggestions for today with some favorable track record? Or suggestions on what to avoid?
William Korthof
Sustainable Solutions Partners
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com<http://www.cometenergysystems.com>
Cell: 264.235.5670
Skype: netconcepts
________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
<EM4000SX_MINI-01.PDF>_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>
Miller Solar
Voice :805-438-5600
email: william at millersolar.com<mailto:william at millersolar.com>
http://millersolar.com
<http://millersolar.com/>License No. C-10-773985
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P Please think of the environment before printing this email
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130325/8775341f/attachment.htm>
More information about the RE-Wrenches
mailing list