[RE-wrenches] Conductor Sizing for Supply Side Connection
Ross Taylor
wind.trainer at gmail.com
Thu Feb 28 21:24:38 EST 2013
Hi Garrison,
This is a great discussion and I think I've read all the responses. If I
missed this question, please forgive me. But, in your original post you
refer to a 200 amp service. I don't, though, see mention of the rating of
the bus bars. The bus bars may be rated for something more than 200 amps,
depending upon the panel, even if they're protected by a 200 amp main
disconnect. If so, that would increase your backfeed breaker sizing
options.
Best wishes,
Ross Taylor