[RE-wrenches] Conductor Sizing for Supply Side Connection
All Solar, Inc.
allsolar at scswifi.net
Wed Feb 27 16:49:47 EST 2013
There is an exception in NEC2011 regarding the point of connection. This may not apply, but you could avoid the supply side. 4500W / 240V = 18.75 x 1.25 = 23.4A, well under the 120% rule. reference 705.12(D)(2)
Jeremy
All Solar
CO,USA
----- Original Message -----
From: Garrison Riegel
To: 'RE-wrenches'
Sent: Wednesday, February 27, 2013 2:15 PM
Subject: [RE-wrenches] Conductor Sizing for Supply Side Connection
Wrenches,
On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A service, and I'd very much appreciate some advice if y'all are willing.
Since the inverter output OCPD is required to be 60A we are looking at a supply side connection, and I have two questions:
1. Before the point of interconnection the inverter output circuit will first pass through the XW Power Distribution Panel and inverter bypass, which is essentially a 60A breaker. The service disconnect for the supply side connection will also be fused at 60A. Does the 120% rule apply to the conductor between these two OCPDs? Or since this is a supply side connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this AHJ is on the 2008 NEC]
2. Can anyone recommend a reliable insulation piercing tap connector? Or would you recommend something else entirely for a residential supply side connection?
Thanks in advance,
Garrison
847-677-0950
Solar Service Inc.
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130227/7867bf2e/attachment.htm>
More information about the RE-Wrenches
mailing list