Chris,
It sounds like you are creating a generator supplied mini grid, if I
understand correctly, My reading is that your generator is creating
the AC voltage, and the inverter is synchronizing with it, allowing
power to be fed into the system from a PV source.
This approach could represent a major innovation in solar
industry. I remember a decade or so ago when it was proposed, on
this list, that battery based inverters could be backfed to charge
batteries, and someone tried it. It worked. Today AC coupling is
standard operating procedure.
Up to that time, it was only understood that to connect an AC source
to the output of a battery based inverter could damage it. Maybe the
next step is to AC couple to generator supplied sub panels and allow
PV usage during power outages.
What inverter and generator are you using? How many Watts of PV are connected?
Thank you,
Drake
At 02:04 PM 2/10/2013, you wrote:
>I have a generator and PV system that just works together, despite
>all the dire predictions that it won't. from my experience of PV and
>generators (I am also a generator tech), the biggest issue is the
>AVR board and how it responds to back fed voltage, and the generator
>controller's over voltage settings.
>I think that it would probably on only require a reprogrammed
>inverter to make this work as follows.
>The AVR produces excitation voltage to vary the strength of the
>rotor field and therefore the induced voltage in the stator. When
>the PV system back feeds the generator, the excitation level is
>reduced to control the voltage. When there is no load, the inverter
>keeps raising the voltage to attempt to push the current to the grid
>and at some point the generator trips out on overvoltage.
>
> If the inverter was programmed to reduce the production of power
> in response to the rise in voltage, it would sync pretty nicely
> with the generator. However, this would likely violate the IEEE
> parameters for a grid tied inverter. SMA has off-grid mode, I
> suspect that is the best solution.
>
>In a Sunny Island system, as I understand it, the Sunny Island
>caries the frequency to communicate to the inverter to reduce the
>current output. That avoid the problem of the inverter raising the voltage.
>
>
>
>
>On Sun, Feb 10, 2013 at 2:45 PM, Drake
><<mailto:drake.chamberlin at redwoodalliance.org>drake.chamberlin at redwoodalliance.org>
>wrote:
>Hi Kevin,
>
>Thanks for the Eigg video. What a great place.
>
>I didn't see evidence of any AC coupling of inverter produced AC to
>a generator produced mini grid. I understand this is being done in
>a homebrew manner by some.
>
>The current wisdom on the issue is that the less the PV contribution
>to the generator supplied grid is, the easier. It would seem that
>if a grid tie inverter output could be regulated, using Sunny Island
>type controls, it should be possible to have a small inverter
>generator create a mini grid that could be fed by PV.
>
>A system featuring this type of technology was linked in a posting
>on this list some years ago, The link seems dead now. In that case
>a large generator was feeding a number of houses, and PV was fed
>into the system.
>
>The reason for this interest is that battery backup systems are much
>more expensive than generators. We need to find a way to utilize PV
>arrays during outages without the expense of battery backup systems.
>
>Drake
>
>
>
>At 07:42 PM 2/8/2013, you wrote:
>Hi Drake,
>
>SMA has very good solutions for this. Does this out of the box
>without a bunch of custom control systems. I have put a few systems
>in like this, but the renewables not yet online (generator / battery
>now). If you google Isle of Eig you will find some info on what they
>have done there.
><http://islandsgoinggreen.org/about/eigg-electric/>http://islandsgoinggreen.org/about/eigg-electric/
>
>Kevin
>
>-----Original Message-----
>From:
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of Drake
>Sent: February 8, 2013 6:41 AM
>To: RE-wrenches
>Subject: [RE-wrenches] Generator Controlled Mini Grid
>
>
>A potential customer is interested in a mini grid, set up by a
>generator, to connect his array to.
>
>Some years back, on this list, an article was linked about a
>community with a central generator that had PV input to the generator
>supplied, local grid, using electronic controls.
>
>Has any progress been made in this technology? Does anyone have a
>link to the electronic control equipment or any other relevant information?
>
>Thanks,
>
>Drake
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>
>--
>Chris Mason
>President, Comet Systems Ltd
><http://www.cometenergysystems.com>www.cometenergysystems.com
>Cell: 264.235.5670
>Skype: netconcepts
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130211/c7db2b3a/attachment.htm>
More information about the RE-Wrenches
mailing list