[RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibility question

boB boB at midnitesolar.com
Sat Feb 2 21:56:32 EST 2013


Carl,   NZ is 240 VAC right ?   240 VAC 2 wire ?

I think that the problem may have to do with leg to leg voltage cross 
regulation
imbalance in 120/240 3 wire systems.

boB


On 2/2/2013 3:23 PM, Carl Emerson wrote:
>
> Goodness knows why 240V Sunny Island's are unavailable in the US...
>
> We have been installing these in NZ for years !!!
>
> Regards
> Carl Emerson
>
> On 2/1/2013 7:42 AM, John Berdner wrote:
>
>> John:
>>
>> If doing an AC coupled system with SB/SI there a couple things to 
>> consider.
>>
>> 1)SI is 120 Vac only and SB and grid are both 240. You can get 2 SI's 
>> but that is pricey.  SMA now makes an autoformer (finally) but it is 
>> really big and pretty expensive (hey Robin/Bob there is an 
>> opportunity here).  Too bad they don't make a 240 Vac SI and no 
>> longer make the old 1800 which had a 120 Vac  output.
>>
>
>
> Already doing that, John, as part off our SMA/SI/SB  and battery based 
> integration package just starting to ship now.
>
> Thanks !!
> boB
>
>
>
> A couple of ways to wire this (ASCII Draw, >> indicate power flow, <> 
> indicates bidirectional):
>
> PV >> SB >> Protected Load Center <> Auto former <> SI <> Xfer switch 
> <>Grid.
>
> |                                            |
>
>   | >> Loads                                              | <<<  Generator
>
> Or alternatively like this:
>
> PV >> SB >> Protected Load Center <> Xfer switch <>Auto former <> SI 
> << Generator
>
>                       |                      |
>
>  | >> Loads            | <>  Grid
>
> A couple of tradeoffs here:
>
> In case 1 the downside is that the output of the SI  is 120 Vac to the 
> grid = imbalance.  All your grid tied PV flows through the auto-former 
> with the associated losses.  The upside is that your protected loads 
> are protected by the SI which has a very fast (transparent) transfer.
>
> In case 2 the downside is that the loads are not protected so you will 
> see an interruption when the xfer switch transfers.  With a manual 
> xfer switch this interruption could be a long time J  The upside is 
> the PV is connected directly to the grid @ 240Vac normally with no 
> autoformer losses
>
> If the SI is already installed you probably are doing something like 
> this already.
>
> To connect in a generator you have to understand the SI's grid input 
> programming. The SI has only one physical grid "input".  I say "input" 
> because both side of an SI are bi-directional and can be either and 
> input or an output depending on power flow. If you go with Case 1 The 
> problem is that you need to set the current limit high enough for the 
> SB so it can grid feed.  If your SB is larger than your generator you 
> can overload the generator when in backup mode.  You also need to 
> allow power flow out of the grid input which you don't want with a 
> small generator.  It is also nice to have wider voltage and frequency 
> limits when operating with the generator.   Fortunately there are 2 
> logical inputs for the single grid input and a digital generator mode 
> selector input (signal level) that is used to switch between the two. 
> Each of these logical inputs can have different parameters, i.e. one 
> for grid and one for generator.  You provide a feedback a signal to 
> the digital input mode selector to tell the SI which set of parameters 
> to use.
>
> There are several ways to do the mode selection ranging from a switch 
> (light switch or toggle switch) near the SI to select modes to an aux 
> contact on a full auto xfer relay.
>
> For a low case bulletproof approach use a 3 phase manual xfer switch 
> and use the unused third power pole to do your digital input mode 
> switching. This is what I have at my house.  The grid feeds one side 
> of the manual Xfer switch and I have an SO cord on the other side to 
> plug in to a generator for charging during a prolonged outage.
>
> Feel free to contact me either online or offline if you have questions.
>
> Best Regards,
>
> John Berdner
>
> General Manager, North America
>
> SmallBannerPictEngnew
>
> SolarEdge Technologies, Inc.
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of our 
> new address.)/*
> T: 510.498.3200, X 747
>
> M: 530.277.4894
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org> 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *john
> *Sent:* Friday, February 01, 2013 4:12 AM
> *To:* re-wrenches at lists.re-wrenches.org 
> <mailto:re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524 
> Compatibility question
>
> John,
>
>    Thanks for that bit of information.  I have a customer with a 
> SB5000 and recently added a Sunny Island with 8 L16 batteries.  This 
> answers their question as to what they will do in an extended outage 
> with no sun. I wanted to suggest a small backup generator but wasn't 
> sure how it would work.  Now I can install the cord and set the sunny 
> island for a Honda 2000i, several of which I keep on hand for 
> emergency power for us and our customers.
>
> John Blittersdorf
>
> /NABCEP Certified Solar PV Installer ^tm /
>
> *Central Vermont Solar & Wind LLC*
>
> 104 River Street
>
> Rutland, VT 05701
>
> 802-770-8625 Cell
>
> 802-747-0577 Office
>
> 802-773-0924 Fax
>
> Mark your calendar:  SolarFest 2013,  July 12, 13 & 14 
> www.SolarFest.org <http://www.solarfest.org/>
>
>
> -----Original Message-----
> From: John Berdner <John.Berdner at solaredge.com 
> <mailto:John.Berdner at solaredge.com>>
> To: Allan <Allan at positiveenergysolar.com 
> <mailto:Allan at positiveenergysolar.com>>; RE-wrenches 
> <re-wrenches at lists.re-wrenches.org 
> <mailto:re-wrenches at lists.re-wrenches.org>>
> Sent: Thu, Jan 31, 2013 8:20 pm
> Subject: Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility 
> question
>
> SMA Sunny Island also does this but also discharges battery in 
> parallel with the generator to create a "virtual generator" that is 
> larger than the actual generator.
>
> Just set the max generator current and it does the rest.
>
> Best Regards,
>
> John Berdner
>
> General Manager, North America
>
> SmallBannerPictEngnew
>
> SolarEdge Technologies, Inc.
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of our 
> new address.)/*
> T: 510.498.3200, X 747
>
> M: 530.277.4894
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org> 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org?>] *On Behalf Of 
> *Allan Sindelar
> *Sent:* Thursday, January 31, 2013 2:14 PM
> *To:* William Miller
> *Cc:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility 
> question
>
> William,
> Yes, that's my understanding. Outback acknowledged this to me years ago.
> Allan
>
> *Allan Sindelar*
> Allan at positiveenergysolar.com <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> *Positive Energy, Inc.*
> 3209 Richards Lane (note new address)
> Santa Fe, New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
>
> On 1/29/2013 9:28 PM, William Miller wrote:
>
>     Allan:
>
>     Could it be that the SW systems are protecting the generator with
>     Generator Support, and the Outback inverters are not?
>
>     William Miller
>
>
>
>     At 07:18 PM 1/29/2013, you wrote:
>
>     This is going back several years...
>
>     The Outback VFX series lacks the tight input current regulation of
>     the SW series, so the max AC amps in is really just a suggestion.
>     In many cases (and especially with these small generators) we want
>     to set the max amps in as high as possible to minimize charging
>     time and maximize C/rate. Yet a surge load can momentarily exceed
>     the max amps setting.
>
>     I have observed that the Honda inverter/generators have a quite
>     sensitive AC output breaker, that will sometimes trip if a surge
>     load (such as a refrigerator) comes on during a charge cycle set
>     close to the generator's capacity. This incident was specific to a
>     Honda 3000i. In contrast, Yamaha's EF3000iSE will lug when
>     overloaded - not good for the generator, but also not likely to
>     trip the output breaker.
>
>     This is a different issue than was being discussed, but fits your
>     question.
>     Allan
>
>
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130202/d7fe8767/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13992 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130202/d7fe8767/attachment.jpe>


More information about the RE-Wrenches mailing list