  Dan,
    You may be do this as well, but I frequently deal with homeowners 
with inexpensive generators, I find that the Outback and Magnum 
inverters are very tolerant but I do generally have to load the 
generator up to where I want it bulk charging the batteries, then adjust 
the generator speed to dial in the freqency to 60Hz using the throttle 
adj.  screw.
    Do you find the Iota chargers can reach bulk charge voltages, or 
even EQ voltages ?

     Carl Hansen

On 1/27/2013 5:15 PM, Dan Fink wrote:
> We have run into many problems on very remote sites with various 
> really nice, small newer inverter/chargers not accepting waveforms 
> from various newer (inverter-based) generators. For example on one 
> particular system Honda 1000i works fine, Honda 2000i works fine, 
> Honda 3000i and the charger says "no." Plug a different Honda 3000i 
> into the the same inverter/charger, works fine. After sling-loading 
> the Honda there by helicopter. Arrrrrgh! Inverter makers have been 
> very helpful but the settings just can't be tweaked that far, RE 
> Wrenches list gurus have been awesomely helpful, Honda not so helpful 
> but at least honest.
>
> My service calls by helicopter this year will include an O-scope. I 
> really want to get to the bottom of the problem. It plagues us. I like 
> Iota  chargers more and more every summer.
>
> -- 
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342 (voicemail)
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130127/aefb19ea/attachment.htm>


More information about the RE-Wrenches mailing list