[RE-wrenches] Bonding bushings?

Alex Cozine acdc.cozine at gmail.com
Fri Jan 25 10:51:25 EST 2013


Just ran in to that.  two foot EMT raceway from a production meter into the
grid panel.  we had to take it out of the emt and run it on the outside to
make the inspector happy, I mean, to meet code.


On Thu, Jan 24, 2013 at 10:22 AM, August Goers <august at luminalt.com> wrote:

> Jesse,
>
> Any metallic raceway that has a GEC running through it needs bonding. So,
> if you've got the Enphase DC-GEC running through it then, yes, it would
> need bonding fittings. At least that's my take on it.
>
> Check out NEC 250.64(E) towards the second half of the paragraph. 2011 NEC
> has a nice clarification point and directs you to 250.92(B)(2) through
> (B)(4).
>
> Best,
>
> August
>
>
> August Goers
>
> Luminalt Energy Corporation
> 1320 Potrero Avenue
> San Francisco, CA 94110
> m: 415.559.1525
> o: 415.641.4000
> august at luminalt.com
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jesse Dahl
> Sent: Thursday, January 24, 2013 8:45 AM
> To: Wrenches
> Subject: [RE-wrenches] Bonding bushings?
>
> If you are using micro inverters and terminating them in an AC combiner
> panel, does the feed for the AC combiner panel (125A) need to have bonding
> bushings for the ground wire?  In other words is this ground wire a
> GEC/Equipment ground like might be used if running an inverter output to a
> panel?  The raceway is already in and is EMT.
>
> Thanks!
>
> Jesse
>
> Sent from my iPhone
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Alex Cozine
NABCEP Certified Solar PV Installerâ„¢
Journeyman Electrician

Brothers Electric Solar
brotherselectricsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130125/9af2e784/attachment.htm>


More information about the RE-Wrenches mailing list