[RE-wrenches] GEC for Micro-Inverters and ACPV Modules

Brian Wiley btwinfinity at gmail.com
Thu Jan 17 17:31:13 EST 2013


Hi John,

You have brought up several points.

1. practical answer
The NEC says that a GEC can be solid aluminum. PV mounting rails are 
typically aluminum. It is easy to calculate the ampacity of a solid 
aluminum piece from its cross-section.
Even the lightest rails on the market have an ampacity that is an order 
of magnitude greater than the copper wires required by code for GECs.
The 2011 NEC, section 250.64(C)(3) says that "Bolted, riveted or welded 
connections of structural metal frames ... of structures" are permitted 
splices for the GEC.
The WEEB is a tested and characterized device and therefore preferable 
to one that, while allowed by code, has not been characterized at all.

2. listing
There is no standard to list equipment for use as a GEC or an EGC. The 
lack of a standard does not mean equipment is not suitable, it just 
means we need to use good engineering judgement until the codes catch up.
Does new equipment meet the intent of the existing code? Are there any 
valid engineering reasons not to use new equipment? I think those are 
the questions we should focus on.
Note that the WEEB was introduced almost 7 years ago and these code 
issues still have not been resolved to everyone's satisfaction.

3. connecting to a copper wire
Jason Szumlanski discussed this already, but I will reiterate. When you 
connect a GEC to a string inverter it is done in a reversible manner, 
typical with a screw connection. When you connect to a PV system, 
consisting of multiple distributed inverters, you can do so with a 
reversible connection, typically a listed lug, anywhere on the PV system.

Best Regards,
Brian Wiley



On 1/17/2013 10:58 AM, John Berdner wrote:
>
> Jay:
>
> You raise an interesting question.
>
> I believe the structure would have to be evaluated and Listed for 
> equipment grounding (UL is working on a new Standard for this now) AND 
> for use as a GEC (which I don't think is possible).
>
> Even if the WEEB was approved for use as a GEC (I still do not feel 
> this is the case) the rail then needs to be contiguous or irreversibly 
> spliced to the copper GEC.
>
> I am not aware of any Listed hardware that facilitates this.
>
> Anyone know of any ?
>
> We also have a dissimilar metals problem irreversibly crimping or 
> exothermic welding (the Code requirement) copper to aluminum.
>
> Best Regards,
>
> John Berdner
>
> General Manager, North America
>
>
> Solaredge Technologies, Inc.
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of our 
> new address.)/*
> T: 510.498.3201 ext 747
>
> M: 530.277.4894
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *jay 
> peltz
> *Sent:* Wednesday, January 16, 2013 8:52 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules
>
> Dear John and Brian
>
> Thanks for a great discussion.
>
> My question is:
>
> If you used a WEEB to connect the inverter to the rail, is the rack 
> rail listed as a GEC?
>
> Or does it have to be listed as a GEC?
>
> Thanks
>
> Jay
>
> Peltz power
>
>
>
> Sent from my iPad
>
>
> On Jan 16, 2013, at 12:09 PM, Brian Wiley <btwinfinity at gmail.com 
> <mailto:btwinfinity at gmail.com>> wrote:
>
>     Hi John,
>
>     I don't feel that you are argumentative. I am glad for this forum
>     and people to put forth honest opinions.
>
>     I think you just may not be aware of how the WEEB actually works.
>     It is a type of rivet, not just a pronged thing that makes
>     connection as part of a bolted connection.
>
>     It does use a bolt to engage the part, but the teeth on the WEEB
>     are specially shaped. When the bolt is torqued, the teeth deform,
>     similarly to a rivet.
>     The metal that it is connecting to mushrooms up around the tooth
>     and the tooth pinches in around the metal.
>     This deforming action is what forms an exceptional electrical
>     connection and also forms an air-tight seal between the part and
>     embedded metal to resist corrosion.
>
>     If you remove the bolt, the WEEB will still be connected to the
>     metal. You must forcibly remove the WEEB from the metal.
>
>     Hope that clears things up for you.
>
>     Best Regards,
>     Brian Wiley
>
>
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended 
> only for the use of the individual or entity who is the intended 
> recipient and may contain information that is privileged, confidential 
> and exempt from disclosure or any type of use under applicable law. If 
> the reader of this e-mail is not the intended recipient, or the 
> employee, agent, or representative responsible for delivering the 
> e-mail to the intended recipient, you are hereby notified that any 
> dissemination, distribution, copying, or other use of this e-mail is 
> strictly prohibited. If you have received this e-mail in error, please 
> reply immediately to the sender.
>
> *P*  Please think of the environment before printing this email
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20130117/0b43874c/attachment.htm>


More information about the RE-Wrenches mailing list