[RE-wrenches] Point of Connection 705.12D2 Exception
Gary Willett
gary at icarussolarservices.com
Sun Dec 30 18:41:46 EST 2012
Jeremy:
The XW-6048 spec for maximum AC Input Current (maximum 75% imbalance
between L1-N, L2-N) is:
L-N: 41.2 A L-L: 27.5 A
So, with a Line to Neutral current of 41.2A x 1.25 = 51.5A or rounds up
to 60A 2-pole breaker.
This condition could occur in a grid-tied configuration when the
inverter is in AC BYPASS mode and the batteries are being charged from
the grid.
Regards,
Gary Willett
On 12/30/2012 4:48 PM, Jeremy Rodriguez- All Solar Inc. wrote:
> Ok, so 35A min., but what about maximum?
> A 200A mains panels allows 120% max back feed correct?
> Confused.....
> Jeremy
> All Solar
> Sent via BlackBerry. Sorry for typos and shorthand!
>
> -----Original Message-----
> From: John Berdner <John.Berdner at solaredge.com>
> Date: Sun, 30 Dec 2012 23:54:17
> To: allsolar at scswifi.net<allsolar at scswifi.net>; RE-wrenches<re-wrenches at lists.re-wrenches.org>
> Subject: RE: [RE-wrenches] Point of Connection 705.12D2 Exception
>
> Jeremy:
>
> 31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp breaker would be the minimum size per Code.
> The inverter may have a higher "pass through rating" to support the loads and so is likely the reason a 60 Amp breaker is specified.
> The pass through rating is typically based on the size of the isolation relay and is usually higher than the inverter's continuous power rating.
>
> Best Regards,
>
> John Berdner
> General Manager, North America
>
>
>
> 3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.)
> T: 510.498.3201 ext 747
> M: 530.277.4894
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeremy Rodriguez- All Solar Inc.
> Sent: Sunday, December 30, 2012 10:35 AM
> To: re-wrenches at lists.re-wrenches.org
> Subject: [RE-wrenches] Point of Connection 705.12D2 Exception
>
> Wrenches,
> Since the XW6048 calls for a 60A breaker to feed the inverter input and we are connecting back to the load side of a 200A panel is this correct. 6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker? Help me understand this.
> Jeremy
> All Solar
> Sent via BlackBerry. Sorry for typos and shorthand!
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
> P Please think of the environment before printing this email
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121230/d258c0b8/attachment-0001.htm>
More information about the RE-Wrenches
mailing list